I am currently designing some circuits for large convenience store and I have a question about the thermal insulation derating factor. A radial circuit will feed two display fridges, total load 10A. The circuit will run from the DB through the roof space on a perferated tray to the back of the shop. It will then be installed inside a 50mm aluminium stud wall with thermal insulation.

My question is, do I de-rate the cable by half as it's running from ceiling to floor level? (in excess of 500mm)

Or

Calculate without Ci and choose ref method 102?

Thanking you in anticipation
 
Hi - which factor to use depends on exactly how the cable passes down the wall. From what I’ve understood, it seems it’s either IM102 or (more likely) 103, from Table 4A2. This leads us to Table 4D5 and the various ratings. As you say, 103 is 50% of Clipped Direct and that’s what I’d probably use.
 
2.5mm radial will allow you 13A as a worst case of derating (ref. 103), so that's what i'd fit. probably OCPD 16A.
 

Reply to Cable calculation - Derating factors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
Hi This is about a design problem in an assignment. A cable basket containing several circuits passes horizontally through an internal concrete...
Replies
9
Views
2K
I'm looking at adding 100mm of sound insulation in an internal floor with 9x2" joists. The house has been rewired at some point so there are...
Replies
3
Views
1K
Im Working on a new build site at the moment, and the kitchen layout has changed to include an island with a hob on it. Meaning im goin to have...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock