How deep you bury the duct depends on the risk of it being damaged. Some of the figures mentioned (e.g. 60cm) are those used by the DNO (electricity suppliers) for carriageway use, but it is 45cm for under a footpath (and 1-1.2m for ploughed arable land), and those are not mandatory on private land / private circuit. Depth is to the top of the duct.
You can run CAT-5/6 cable in the same duct safely as the power cable as the steel armour is earthed and acts as a screen for noise, but get cable that is tough enough for outdoor use. For example:
If you really want high speed (above 1Gbit/sec) then putting in fibre would be best, but I don't know much about getting it in a cable form tough enough to pull through (you can, I have seen it, but never had to order any!).
If you plan for an EV charging point then the main difference is the power demands. Typically an out building with a few 13A sockets and lights will only be needing 10-20A and often you would get away with 4mm cable at that distance. But if you plan on having a 7kW charger or more then you are adding 30A to that to begin with and so would need heavier SWA cable, perhaps up to 10mm or so.
You can often pull through a 2nd run if the EV is added later, and you might just want that if separate circuits anyway, so it is something to discuss with the electrician. It is easier to pull all through at once if you can, so even if the EV is delayed having a cable in is just the cost of the wire which is around £4-5/m for that sort of size.
Also mentioned is earthing and your power supply type, if there is metalwork in the out building and you are on a TN-C-S supply then you need either 10mm earth bonding cable (achieved with the EV-sized cable, or an additional earth wire if smaller used) or you put in an earth rod and have a TT supply at the outbuilding. Hence the real need to discuss the details with your electrician before committing to cable installed.
[automerge]1588435396[/automerge]
In the ideal case you would run just one power cable big enough for everything you might need and have separate circuits at the garage CU. That leads to the lowest overall installation cost and greatest selectivity in faults not taking out healthy circuits.
That might need a CU bigger than the usual "garage" sort that only has 2 breakers and an RCD, so it is something to plan from the start as you electrician could easily fit a small home-style CU with things like surge protection as well as plenty of space for the future use.