hi im redoing the bathroom and the 9.5kw shower is on this cable which has burnt at the connector block at some point its on a B32 MCB

im not sure what size this cable is, measuring the cable width it looks to be 6mm2 measuring the conductor looks to be a 10mm2

the diameter of the individual conductors is between 4-5mm

the width of the overall cable is about 14mm

the earth is significantly smaller, slightly thicker than a 2.5mm2 conductor

pictured next to 2.5mm2 cable for comparison

when i put everything through the IEC calculator it says the earth size should be the same as live and neutral cable wrong anyway?
 

Attachments

  • 1.jpg
    269.2 KB · Views: 16
  • 2.jpg
    273.6 KB · Views: 18
  • 3.jpg
    266.2 KB · Views: 18
  • 4.jpg
    66.1 KB · Views: 18
With twin and earth cable, the cpc (earth) is smaller…. Perfectly ok.

I would say it’s 6.00mm as it’s a solid cpc (2.5mm size)
With 10mm, the cpc is stranded (4.0mm size)


just curious, but where was that connector block?
 
2nd pic of burnt out terminals recently

Common problem

I reckon plumbers and DIY are responsible for most of it, most trained sparks know to tighten the connections
 
I just find it strange that a plastic connector is screwed down like that…. And I know that’s the way everyone does it.
Metal screw possibly cutting into the plastic, reducing the insulating material and creating a weakened path between the live copper and the cpc through the screw.

Not the problem here, I should add.

This is simply a loose connection causing heat
 
I’m 99% sure it is looking at that, as above comparing the 2.5mm cpc with the 2.5mm T+E it looks spot on.

(If you have a micrometer you can just halve the measurement of a single strand, multiple by itself then PI, then by the number of strands (usually 7) to double check.)
 
Just a thought…. Have a look on the grey sheath of the cable, it sometimes has the size marked into it
Instead of mucking around cutting strands etc, try and work out the cable route distance, measure the resistance, look in the OSG or 7671 and check th /e mili ohm per meter and work it out from that. just a thought.
 
Instead of mucking around cutting strands etc, try and work out the cable route distance, measure the resistance, look in the OSG or 7671 and check th /e mili ohm per meter and work it out from that. just a thought.

If he doesn't know whether a cable is 6mm or 10mm then I suspect he's not going to have a copy if BS7671 and an Ohmeter. I don't think the OP is a spark Pete.
 
If he doesn't know whether a cable is 6mm or 10mm then I suspect he's not going to have a copy if BS7671 and an Ohmeter. I don't think the OP is a spark Pete.
He says he is a trainee electrician
If he doesn't know whether a cable is 6mm or 10mm then I suspect he's not going to have a copy if BS7671 and an Ohmeter. I don't think the OP is a spark Pete.
The OPs profile says he is a Trainee Electrician and has 2365 so deductions would say he should own or have accessv to BS 7671 BUT YOUR POINT IS A VALID ONE
 

Reply to cable identification(shower) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K
Hello Looking for some guidance please. Lived in current house just over a year now and had couple issues with our pull cord switch (45A)...
Replies
49
Views
5K
Deleted member 9648
D
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
We recently had a thread or two about some cables that were almost certainly tinned copper, but people continued to suspect they were aluminium...
Replies
7
Views
2K
S
I am about to embark on a project to convert the top floor of my garage into a small granny annexe. There are lots of considerations to make, but...
Replies
11
Views
5K
TallPaul
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock