Morning....

I have a friend of a friend who is just looking for some advice regarding his 12V solar set up.

It's a metal shed approx 5m x 3m.

My 2 questions are:

1. Does the cable joining each of the 5 batteries have to be 50mm as well as the cable from battery to 3kW inverter? I'm sure it does but just wanted to be certain.

2. How to earth this system? I have drawn an earth rod coming from the 230V consumer unit but I realise this is no good by itself. I'm just not sure how this gets joined to the neutral (or which neutral) in order for it to become a working earthing system that would allow the RCD's to trip with earth leakage? (See picture below)

I realise I could have an earth free system (as I have in my wooden shed) but with this being a metal shed that didn't seem like a good idea.

The picture below only shows 1 solar panel, please ignore this as there will be more.
Solar.jpeg
 
Aico 3000 Range
This official sponsor may provide discounts for members

telectrix

-
Mentor
Arms
Esteemed
50mm is optimistic @ 250A. maybe use tri-rated cable. rod looks good and bond the metal structure. the RCDs would get the required earth leakage to trip by means of L-person-earth. that's what they're designed for.also note you'll need 14-15V for battery charging.
 

snowhead

-
Mentor
Cables from Charge controller to first battery need to match the max output and fuse from the charge controller.

Cables from first battery and between others and to the Inverter need to match the max input and fuse.

As Tel says, 50mm may be under.
You'd need to use Vehicle battery cable for that part.

This link shows 50mm at 12v 345amp, but that'll be short duration for starter motors.
They do 70mm.

 

Strima

-
Arms
Esteemed
Have a look a the inverter specs, it might need the chassis of the inverter referencing to earth but it could well be done on the neutral.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #6
Cables from Charge controller to first battery need to match the max output and fuse from the charge controller.

Cables from first battery and between others and to the Inverter need to match the max input and fuse.

As Tel says, 50mm may be under.
You'd need to use Vehicle battery cable for that part.

This link shows 50mm at 12v 345amp, but that'll be short duration for starter motors.
They do 70mm.

50mm is rated at 246A - 275A (Table 4E1A) ref method F so I would have thought ok, especially as the max demand will not be at 250A (12V) for long periods. I'll definitely suggest battery cable though.

50mm is optimistic @ 250A. maybe use tri-rated cable. rod looks good and bond the metal structure. the RCDs would get the required earth leakage to trip by means of L-person-earth. that's what they're designed for.also note you'll need 14-15V for battery charging.
I thought the earth rod had to have some link back to the supply neutral? In a home which is TT the neutral is linked to earth somewhere which i thought meant any earth fault going through the TT rod has a pathway back to the supply neutral and will therefore be a effective earthing system. otherwise its just a copper rod in the ground.

Lucien and Davesparks tried explaining this to me sometime ago with my shed but I didn't quite get it!
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #8
which beggars the question....... would it not be cheaper to run a 40A supply from the house?
It's not by a house. It's out in the country at a plant nursery. There are Mains voltage electrics in a giant greenhouse fairly nearby but he wants to have a play with solar.
 

davesparks

-
Mentor
Arms
Esteemed
50mm is optimistic @ 250A. maybe use tri-rated cable. rod looks good and bond the metal structure. the RCDs would get the required earth leakage to trip by means of L-person-earth. that's what they're designed for.also note you'll need 14-15V for battery charging.
There won't be a path via the person to earth if one pole of the supply isn't connected to earth.
 

davesparks

-
Mentor
Arms
Esteemed
Depending on the layout and method of actually connecting to the battery you could use a solid copper or brass bar across the top which bolts to each one (assuming it's some sort of bolted connection)
When I put twin batteries in my landrover I used offcuts of lightning conductor to link the batteries.

Or just thinking out loud you could maybe have two copper bars mounted either side of the row or batteries used as busbars, then short cable to each battery terminal. You'd probably be able to use smaller cables then and make it easier to swap out batteries.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #11
Depending on the layout and method of actually connecting to the battery you could use a solid copper or brass bar across the top which bolts to each one (assuming it's some sort of bolted connection)
When I put twin batteries in my landrover I used offcuts of lightning conductor to link the batteries.

Or just thinking out loud you could maybe have two copper bars mounted either side of the row or batteries used as busbars, then short cable to each battery terminal. You'd probably be able to use smaller cables then and make it easier to swap out batteries.
Thanks for the suggestion Dave.
Could I ask your opinion on the earthing side of it?
Is it as simple as putting in another rod going from the neutral on the 12V side of the inverter? This is a guess as I just don't understand the principle properly.

I cant understand why the RCD has to have an earth to trip. If I was to touch the live cable (line) and there was no earth, as long as >30mA of current travelled through me (to the general mass of the earth) then the RCD would detect an imbalance and trip, wouldn't it? On a lighting system in a house without an earth the RCD would still trip if you touched the line ( assuming >30mA again).
 
Last edited:

buzzlightyear

-
Arms
Esteemed
it would be better to get a genny in or his a tree hugger .
 
D

Deleted member 26818

Thanks for the suggestion Dave.
Could I ask your opinion on the earthing side of it?
Is it as simple as putting in another rod going from the neutral on the 12V side of the inverter? This is a guess as I just don't understand the principle properly.

I cant understand why the RCD has to have an earth to trip. If I was to touch the live cable (line) and there was no earth, as long as >30mA of current travelled through me (to the general mass of the earth) then the RCD would detect an imbalance and trip, wouldn't it? On a lighting system in a house without an earth the RCD would still trip if you touched the line ( assuming >30mA again).
No.
You are earthing the 230V, so the return is to the 230V side of the inverter.
You would need the neutral output from the inverter, referenced to earth, which it probably already is.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #14
No.
You are earthing the 230V, so the return is to the 230V side of the inverter.
You would need the neutral output from the inverter, referenced to earth, which it probably already is.
When you say referenced to earth could you explain that a little more? 'Referenced' can't mean the same as 'connected' otherwise that would mean just connecting the same earth rod to the 'neutral in' terminal on top of the main switch in the CU.
How do I achieve this 'reference' to earth? How can the inverter already be referenced to earth if it is not in contact with earth in any form?
 

davesparks

-
Mentor
Arms
Esteemed
.

I cant understand why the RCD has to have an earth to trip. If I was to touch the live cable (line) and there was no earth, as long as >30mA of current travelled through me (to the general mass of the earth)
Where is the 30mA current going to flow to? For current to fow there must be a complete circuit, if the supply is not connected to the general mass of earth then the current cannot flow to via the general mass of earth.

If you don't have the N - E link then if you make contact with the L whilst in contact with the earth no current will flow and you will not receive a shock, this is the principle of how isolated supplies, shaver sockets etc work.
This is all fine for something simple like a shaver socket, or a single piece of equipment fed from an isolating transformer. But it can be a problem if you try to use this for an installation, the first time a fault occurs between any conductor and exposed metal (known as the first fault) will not present a danger but will be undetected.
If another fault occurs it becomes very dangerous
 

davesparks

-
Mentor
Arms
Esteemed
When you say referenced to earth could you explain that a little more? 'Referenced' can't mean the same as 'connected' otherwise that would mean just connecting the same earth rod to the 'neutral in' terminal on top of the main switch in the CU.
How do I achieve this 'reference' to earth? How can the inverter already be referenced to earth if it is not in contact with earth in any form?
Referenced does in this case mean connected, you would be installing the N-E link at the point of your choosing. The easiest place is probably as you say, at the DB where you would link the neutral to the earth bar, this is the same as putting the N-E link in a large switchboard as seen in industrial or big commercial installations where they are fed from their own transformer.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
The inverter may already have a neutral-earth connection inside. Or, some other point of its internal circuit may be earthed, to the socket, the case or both. You need to check the manufacturers' data which might or might not say. The connection needs to be solid, and made at the source, then the resulting CPC referenced to earth with the rod. Don't earth via the DC side, treat that as floating although it might not be within the inverter.

As DS says, the problem with having an RCD without an earthed neutral is that it won't react when a single fault or latent leakage path occurs, nor will you get a shock, so you don't know that the fault exists. If it is downstream of the RCD as it is likely to be, i.e. at an appliance or in the wiring rather than in the inverter, then when another fault or leakage occurs to the other pole of the supply you have a fault path that doesn't upset the RCD balance, you do get a shock but the RCD still doesn't trip. What is needed is an earthed neutral so that whenever a fault occurs to the line, the RCD trips regardless of whether another fault or a shock path exists.

E2A - when we say earthed neutral, there are two aspects. Both the MET / CPC and the general mass of earth should be connected to the neutral. If one lived in a plastic bubble with no access to earth, shocks would only be to the CPC / casing of appliances rather than true earth. There would then be no need for the mass of earth to be brought into the equation, only the CPC and neutral would need to be connected in order to provide an equipotential and enable the RCD to detect line-CPC faults. But in the real world, where the mass of earth is accessible to the touch, the CPC should be connected to it via the MET to make the equipotential that of earth rather than some arbitrary voltage. Therefore the result is that the neutral is earthed, as well as being connected to the MET. The RCD will then also protect against a shock path from line to true earth, as well as to the CPC.
 
Last edited:

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #18
ps... I should have drawn an extra line coming from the inverter output going to the earthing bar in the CU. i.e it would be a normal plug plugged into the inverter which is the supply to the consumer unit. Does this mean the earthing system would be effective if this earth is referenced to earth in the inverter?
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #19
The inverter may already have a neutral-earth connection inside. Or, some other point of its internal circuit may be earthed, to the socket, the case or both. You need to check the manufacturers' data which might or might not say. The connection needs to be solid, and made at the source, then the resulting CPC referenced to earth with the rod. Don't earth via the DC side, treat that as floating although it might not be within the inverter.

As DS says, the problem with having an RCD without an earthed neutral is that it won't react when a single fault or latent leakage path occurs, nor will you get a shock, so you don't know that the fault exists. If it is downstream of the RCD as it is likely to be, i.e. at an appliance or in the wiring rather than in the inverter, then when another fault or leakage occurs to the other pole of the supply you have a fault path that doesn't upset the RCD balance, you do get a shock but the RCD still doesn't trip. What is needed is an earthed neutral so that whenever a fault occurs to the line, the RCD trips regardless of whether another fault or a shock path exists.

E2A - when we say earthed neutral, there are two aspects. Both the MET / CPC and the general mass of earth should be connected to the neutral. If one lived in a plastic bubble with no access to earth, shocks would only be to the CPC / casing of appliances rather than true earth. There would then be no need for the mass of earth to be brought into the equation, only the CPC and neutral would need to be connected in order to provide an equipotential and enable the RCD to detect line-CPC faults. But in the real world, where the mass of earth is accessible to the touch, the CPC should be connected to it via the MET to make the equipotential that of earth rather than some arbitrary voltage. Therefore the result is that the neutral is earthed, as well as being connected to the MET. The RCD will then also protect against a shock path from line to true earth, as well as to the CPC.
Referenced does in this case mean connected, you would be installing the N-E link at the point of your choosing. The easiest place is probably as you say, at the DB where you would link the neutral to the earth bar, this is the same as putting the N-E link in a large switchboard as seen in industrial or big commercial installations where they are fed from their own transformer.
How can you just join the neutral bar in the CU to the earth bar in the CU? I don't mean physically I mean that it would just cause the RCD to trip as you would have continuity between earth and neutral. In a domestic CU if I made a link between the earth bar and neutral bar this would be a N-E fault and immediate RCD trip.
New diagram below with the earth showing going from plug (inverter) to the earth bar in the CU.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
How can you just join the neutral bar in the CU to the earth bar
You can't. Davesparks actually said:
link the neutral to the earth bar
Meaning the incoming neutral upstream of the RCD, not the neutral bar downstream of it.

Note that the RCD protects against faults on the opposite side of itself to the N-E link because that's how current bypasses it to create an imbalance. Want to protect the installation downstream? Put the N-E link upstream. Linking the neutral and earth bars in the CU downstream of the RCD won't protect the installation, only the inverter upstream of it. Such a link downstream of an RCD will cause an immediate trip on a DNO supply because there is already a link at the substation upstream. Having a link either side of the RCD allows some neutral current to bypass it and create an imbalance.
 
Last edited:

davesparks

-
Mentor
Arms
Esteemed
How can you just join the neutral bar in the CU to the earth bar in the CU? I don't mean physically I mean that it would just cause the RCD to trip as you would have continuity between earth and neutral. In a domestic CU if I made a link between the earth bar and neutral bar this would be a N-E fault and immediate RCD trip.
New diagram below with the earth showing going from plug (inverter) to the earth bar in the CU.
You make the link before the RCD. If you make the link after the RCD it won't work, the RCD certainly wouldn't trip.
If you did it in a domestic installation its completely different, the DNO have already made the N-E link at the substation.

The N-E link being discussed here is effectively the equivalent of the N-E link normally made at the substation by the DNO.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #23
You can't. Davesparks actually said:

Meaning the incoming neutral upstream of the RCD, not the neutral bar downstream of it.

Note that the RCD protects against faults on the opposite side of itself to the N-E link because that's how current bypasses it to create an imbalance. Want to protect the installation downstream? Put the N-E link upstream. Accidentally putting the N-E link downstream won't cause a trip if there's no link upstream (as there would be on a DNO supply), but now the RCD is protecting against faults in the inverter upstream, not the installation.
Oh I see!! So just like a domestic installation where the neutral bar only has continuity with the earth bar when the main switch is closed as it's connected at some point upstream.
So my connection could be between the neutral in the incoming terminal of the main switch (i.e top) in the CU and the earth bar of the CU?
Could I not just check for continuity between the earth and neutral in the inverter by doing a simple continuity check? I'm guessing not as otherwise you would not have said to check the manufacturers data.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #24
You make the link before the RCD. If you make the link after the RCD it won't work, the RCD certainly wouldn't trip.
If you did it in a domestic installation its completely different, the DNO have already made the N-E link at the substation.

The N-E link being discussed here is effectively the equivalent of the N-E link normally made at the substation by the DNO.
Same question to you Dave as asked above to Lucien.

I appreciate you both taking the time to explain this to me.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
Could I not just check for continuity between the earth and neutral in the inverter by doing a simple continuity check
You could, but how would you know whether the continuity is via a small interference suppression component on the PCB, or a heavy cable able to withstand the full output. Chances are, if they are connected, it's OK to put an external link anyway, but there is no guarantee on a consumer-grade inverter how things have been done. If you buy a high-end product such as a Victron or Mastervolt, it will be well engineered and documented.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #26
You could, but how would you know whether the continuity is via a small interference suppression component on the PCB, or a heavy cable able to withstand the full output. Chances are, if they are connected, it's OK to put an external link anyway, but there is no guarantee on a consumer-grade inverter how things have been done. If you buy a high-end product such as a Victron or Mastervolt, it will be well engineered and documented.
I think (I'll use the term loosely) I may be nearing the end of the questions!

So, It would not be a good idea to rely on testing for continuity in the inverter between N and E, therefore i could use a suitable cable to join the neutral and earth as I described in the last post. However, if the inverter does not have a neutral to earth connection in it already is it ok to introduce this connection (i.e N-E link)? Or do all inverters have some form of link between N-E.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
Many cheaper units will have their output floating because they are intended to be used as IT, i.e. with nothing earthed, supplying a single piece of equipment only. This is generally safe as two faults on a single load appliance, from opposite poles of the supply, that do also not connect together within, is very unlikely indeed. Such inverters sometimes state that they must not be used to feed a distribution board or installation. Whether any RFI suppression is defeated by an external link, whether 230V is then imposed on something that doesn't like it, is another matter. It will probably be fine but I'm not prepared to take a wild guess.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #28
Many thanks to both of you (Lucien and DS), it's been an interesting morning :)
 