Discuss Cable size and how to earth this system? in the UK Electrical Forum area at ElectriciansForums.net
HappyHippyDad
Morning....
I have a friend of a friend who is just looking for some advice regarding his 12V solar set up.
It's a metal shed approx 5m x 3m.
My 2 questions are:
1. Does the cable joining each of the 5 batteries have to be 50mm as well as the cable from battery to 3kW inverter? I'm sure it does but just wanted to be certain.
2. How to earth this system? I have drawn an earth rod coming from the 230V consumer unit but I realise this is no good by itself. I'm just not sure how this gets joined to the neutral (or which neutral) in order for it to become a working earthing system that would allow the RCD's to trip with earth leakage? (See picture below)
I realise I could have an earth free system (as I have in my wooden shed) but with this being a metal shed that didn't seem like a good idea.
The picture below only shows 1 solar panel, please ignore this as there will be more.
50mm is optimistic @ 250A. maybe use tri-rated cable. rod looks good and bond the metal structure. the RCDs would get the required earth leakage to trip by means of L-person-earth. that's what they're designed for.also note you'll need 14-15V for battery charging.
Cables from Charge controller to first battery need to match the max output and fuse from the charge controller.
Cables from first battery and between others and to the Inverter need to match the max input and fuse.
As Tel says, 50mm may be under.
You'd need to use Vehicle battery cable for that part.
This link shows 50mm at 12v 345amp, but that'll be short duration for starter motors.
They do 70mm.
Have a look a the inverter specs, it might need the chassis of the inverter referencing to earth but it could well be done on the neutral.
They do 70mm.
50mm is rated at 246A - 275A (Table 4E1A) ref method F so I would have thought ok, especially as the max demand will not be at 250A (12V) for long periods. I'll definitely suggest battery cable though.
I thought the earth rod had to have some link back to the supply neutral? In a home which is TT the neutral is linked to earth somewhere which i thought meant any earth fault going through the TT rod has a pathway back to the supply neutral and will therefore be a effective earthing system. otherwise its just a copper rod in the ground.
Lucien and Davesparks tried explaining this to me sometime ago with my shed but I didn't quite get it!
which beggars the question....... would it not be cheaper to run a 40A supply from the house?
It's not by a house. It's out in the country at a plant nursery. There are Mains voltage electrics in a giant greenhouse fairly nearby but he wants to have a play with solar.
There won't be a path via the person to earth if one pole of the supply isn't connected to earth.
Depending on the layout and method of actually connecting to the battery you could use a solid copper or brass bar across the top which bolts to each one (assuming it's some sort of bolted connection)
When I put twin batteries in my landrover I used offcuts of lightning conductor to link the batteries.
Or just thinking out loud you could maybe have two copper bars mounted either side of the row or batteries used as busbars, then short cable to each battery terminal. You'd probably be able to use smaller cables then and make it easier to swap out batteries.
Thanks for the suggestion Dave.
Could I ask your opinion on the earthing side of it?
Is it as simple as putting in another rod going from the neutral on the 12V side of the inverter? This is a guess as I just don't understand the principle properly.
I cant understand why the RCD has to have an earth to trip. If I was to touch the live cable (line) and there was no earth, as long as >30mA of current travelled through me (to the general mass of the earth) then the RCD would detect an imbalance and trip, wouldn't it? On a lighting system in a house without an earth the RCD would still trip if you touched the line ( assuming >30mA again).
No.
You are earthing the 230V, so the return is to the 230V side of the inverter.
You would need the neutral output from the inverter, referenced to earth, which it probably already is.
No.
When you say referenced to earth could you explain that a little more? 'Referenced' can't mean the same as 'connected' otherwise that would mean just connecting the same earth rod to the 'neutral in' terminal on top of the main switch in the CU.
How do I achieve this 'reference' to earth? How can the inverter already be referenced to earth if it is not in contact with earth in any form?
Where is the 30mA current going to flow to? For current to fow there must be a complete circuit, if the supply is not connected to the general mass of earth then the current cannot flow to via the general mass of earth.
If you don't have the N - E link then if you make contact with the L whilst in contact with the earth no current will flow and you will not receive a shock, this is the principle of how isolated supplies, shaver sockets etc work.
This is all fine for something simple like a shaver socket, or a single piece of equipment fed from an isolating transformer. But it can be a problem if you try to use this for an installation, the first time a fault occurs between any conductor and exposed metal (known as the first fault) will not present a danger but will be undetected.
If another fault occurs it becomes very dangerous
Referenced does in this case mean connected, you would be installing the N-E link at the point of your choosing. The easiest place is probably as you say, at the DB where you would link the neutral to the earth bar, this is the same as putting the N-E link in a large switchboard as seen in industrial or big commercial installations where they are fed from their own transformer.
The inverter may already have a neutral-earth connection inside. Or, some other point of its internal circuit may be earthed, to the socket, the case or both. You need to check the manufacturers' data which might or might not say. The connection needs to be solid, and made at the source, then the resulting CPC referenced to earth with the rod. Don't earth via the DC side, treat that as floating although it might not be within the inverter.
As DS says, the problem with having an RCD without an earthed neutral is that it won't react when a single fault or latent leakage path occurs, nor will you get a shock, so you don't know that the fault exists. If it is downstream of the RCD as it is likely to be, i.e. at an appliance or in the wiring rather than in the inverter, then when another fault or leakage occurs to the other pole of the supply you have a fault path that doesn't upset the RCD balance, you do get a shock but the RCD still doesn't trip. What is needed is an earthed neutral so that whenever a fault occurs to the line, the RCD trips regardless of whether another fault or a shock path exists.
E2A - when we say earthed neutral, there are two aspects. Both the MET / CPC and the general mass of earth should be connected to the neutral. If one lived in a plastic bubble with no access to earth, shocks would only be to the CPC / casing of appliances rather than true earth. There would then be no need for the mass of earth to be brought into the equation, only the CPC and neutral would need to be connected in order to provide an equipotential and enable the RCD to detect line-CPC faults. But in the real world, where the mass of earth is accessible to the touch, the CPC should be connected to it via the MET to make the equipotential that of earth rather than some arbitrary voltage. Therefore the result is that the neutral is earthed, as well as being connected to the MET. The RCD will then also protect against a shock path from line to true earth, as well as to the CPC.
ps... I should have drawn an extra line coming from the inverter output going to the earthing bar in the CU. i.e it would be a normal plug plugged into the inverter which is the supply to the consumer unit. Does this mean the earthing system would be effective if this earth is referenced to earth in the inverter?
How can you just join the neutral bar in the CU to the earth bar in the CU? I don't mean physically I mean that it would just cause the RCD to trip as you would have continuity between earth and neutral. In a domestic CU if I made a link between the earth bar and neutral bar this would be a N-E fault and immediate RCD trip.
New diagram below with the earth showing going from plug (inverter) to the earth bar in the CU.
Reply to Cable size and how to earth this system? in the UK Electrical Forum area at ElectriciansForums.net
Does anyone know the size (diameter) of a reel of 2.5 twin and cpc cable ? i want to put a pole in the van but I don’t have any reels with me here.
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...