Hi we are quoting for installing the main feed for a public swimming pool , its a 3 phase install with 3 no. 300 AMP main fuses . we will be installing a 315 3pn switched fused isolator then SWA on cable tray at a distance of 25 mtrs to the main board , i have allowed for 240 mm2 cable with 70 mm earth am i right or can i install smaller ???
 
Assuming it is XLPE it is plenty big enough. Can you install smaller, I would say yes. You not done any calcs then.
 
Hi we are quoting for installing the main feed for a public swimming pool , its a 3 phase install with 3 no. 300 AMP main fuses . we will be installing a 315 3pn switched fused isolator then SWA on cable tray at a distance of 25 mtrs to the main board , i have allowed for 240 mm2 cable with 70 mm earth am i right or can i install smaller ???

Need more info!

What's your design current, ambient temp and any other factors?!
 

Reply to Cable size check please in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
560

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock