M

MATTMGM

Hi all, looking for a bit of guidance/help please..... I have been asked to confirm the correct cable size on a sub main that supplies the communal area of a block of flats (4 flats in total).

All that is supplied from the consumer unit under the stairs is a 2kw heater, led lights x 6, 2 x cleaners sockets, socket for tv/sky and circcuit for smoke alarms.

The cable is swa buried underground in a duct 25m long.
Consumer unit (under stairs) is 100amp main switch with 63amp rcd.

I have done cable calcs but my calculations seem to be equalling to a small csa.

Thanks for your help.
 
Hi MATMMGM if you don't mind posting your calculations up and results this way any errors can be quickly identified for you and pointed out :)
 
As above mate. If you post up your calculations we can tell you if your are right or where you went wrong. There is no learning in us just telling you the correct size.
 
Is the heater going into a socket or is it going to be fixed via spur.......... separate circuit or coming off the cleaners circuit that is the first thing 16amp MCB?
2 cleaners socket on a radial 16amp MCB?
6 LED lights on a radial 6 amp MCB?
1 socket for sky is this going onto a separate circuit or are you taking it off the cleaners?
FA circuit 6amp MCB?

So next questions are


  • What are you connecting your SWA to ?
  • What is the protection device for the SWA?
  • Are you expecting that all these circuits are going to be energized at the same time?
  • Are you going to apply diversity and therefore size your SWA CPD to that?
 
Hi MATMMGM if you don't mind posting your calculations up and results this way any errors can be quickly identified for you and pointed out :)

Hi, thanks for your reply

i am am at work at the moment but the cable size I got was 2.5mm SWA. Seems a bit small for me ???
 
Hi, thanks for your reply 

i am am at work at the moment but the cable size I got was 2.5mm SWA. Seems a bit small for me ???

And how did you get to this size? Show us your calculations mate.
 
You also need to give a little room for expansion or additions, once you find the correct size cable for the small cost difference I would be sizing up a submain supply in your situe', its not just about what you can get away with cable size wise.
 

Reply to Cable size sub main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
650
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
561
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock