Hi,

Looking for advice,

Doing a new build in a rural location and I’m having to run a mains electricity 500m to the nearest meter.

Had a couple of quotes so far but there vary massively in price.

The first quote the electrician was going to use 16mm cable which even I thought would be too small to account for voltage drop over 500m

Second quote said I needed 300mm cable so obviously there is a huge difference in price.

I know that I’m able to get 3 phase down there and have been told this may be my cheapest options but can anyone offer some advice as I don’t really know who to believe right now.
 
16mm is way out of scale. What is your loading and what volt drop are you allowing for.
 
Volt drop should not exceed 3% for lighting and that is from source of supply to the furthest point of a lighting circuit so the submain if often rule of thumbed at 1%. Given this and the length and anticipated loading 300mm is not large enough. What you propose is unrealistic in real terms.
 
500 meters is a hell of a distance.... As above, speak to the DNO.
 
I calculate roughly you would require 3× 185mm, 4 core cables for a 1% volt drop. Cable cost between £80-85k plus a couple of grand for switch gear.
 
Just go off grid with solar panels , wind turbines and several log burners
 
You need to do some proper loading calculations..
Maximum demand, diversity, etc.
You might be able to use 35mm or 50mm cable.
What equipment will you be powering up?
Other options available such as step up transformers but I feel you are over spec’ the load
 
You need to do some proper loading calculations..
Maximum demand, diversity, etc.
You might be able to use 35mm or 50mm cable.
What equipment will you be powering up?
Other options available such as step up transformers but I feel you are over spec’ the load


Yes one guy I got a quote from has said that I would be able to possible use a 35mm - 50mm 3 phase set up.

It’s just for a 2 bed bungalow, will have an electric shower and cooker
 

Reply to Cable size in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock