Hi guys, can anyone help with this please.
I've a new kitchen going in which will have an induction hob, main oven & a compact oven/ microwave.
Induction hob is 32Amp & 7350W
Main oven is 16Amp & 3450 W
Compact oven 16Amp & 3650 W
New wiring is going in so would it be ok to use 10mm cable on the hob with a 40 amp fuse and a 45 Amp switch. Also a 10mm cable on a different 40 Amp fuse with a 2 way outlet & 45 Amp swich for the two ovens.
Hope I've explained this correctly.
Any help would be appreciated thanks.
 
Bit of an Overkill!
2No 32A circuits would be fine.
As for cable size, depends on route/length/volt drop, derating due to insulation etc.
 
diversity would normally let you use a 32A/6.0mm circuit, so if you use a 10.0mm on a 45A. you'll be fine, even if some itchy-poo on the cable route.
 
diversity would normally let you use a 32A/6.0mm circuit, so if you use a 10.0mm on a 45A. you'll be fine, even if some itchy-poo on the cable route.
I have taken out an old 10mm cable which was linked to a 40A fuse.
Just thought as all the kitchen cables will be renewed the 10mm would be more than adequate but don't want to go over the top as 10mm cable is not cheap.
Yes I'm a yorkshireman lol
 
As DefyG. But I’ve done exactly the same .,10mm to island unit with induction job and same for two ovens...but I do like to over engineer. ??
 
I have taken out an old 10mm cable which was linked to a 40A fuse.
Just thought as all the kitchen cables will be renewed the 10mm would be more than adequate but don't want to go over the top as 10mm cable is not cheap.
Yes I'm a yorkshireman lol
why take it out when you could have re-used it?
 
Without knowing more about routes, de-rates and all that kinda stuff, sounds like 2 x 4mm radials would be fine (and a lot easier to work with).
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
632
I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with...
Replies
3
Views
2K
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
3K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
184
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock