Hi.

Hoping that many of you experienced girls and guys out there will be able to help me out.

A disagreement regarding cable sizes and fuse ratings.

For example : I believe a 2.5mm2 radial ( assuming it is more than 5 metres in length ) should be rated at 16A unless there is convincing evidence that a 20A rating will not induce heating of the cable to an extent that could cause future damage.

As the lesser experienced sparks, my opinions are questioned.

More so with 4mm2 T&E. I believe a 20A rating ( again assuming a measureable run of cable ) rather than a 32A.

My query relates to cables installed as in a standard domestic environment.

Thanks for any thoughts on this matter. :eek:
 
Also i would think the the maxium currents rated in bs 7671 are probally very reduced from what would actually make the cable heat up or melt, take for instance the safe working load of lifting equpiment the item will have to take 7 times its rated swl ie a 1 ton strop should be on its limits at 7 ton but shouldn't break
Hope that put your mind at rest
Regards
AJ
 
ajelec the current rating in the BRB is based at an operatin temperature of 70c as the normal ambient temperature is 25 which means there is a larger C.C.C of a factor of about 1.02 (not 100% sure OSG in van)
 
Hi
Sorry if I’ve posted this in the wrong area.

Do the tabulated values for the current carrying capacity of conductors in bs7671 include the 1.45 rule of thumb?

I.e. a 32amp type B should trip within an 1hr at 1.45x it’s In (46.4amps)

So do I look for a cable that can take 46.4amps, even if the Ib is only 32amps?

I’m sure I’ve seen a reg that states the 1.45 is satisfied when using the tabulated values for twin & earth.

This is all hypothetical and I’m trying to keep my question simple (leaving out the other correction factors and install method)

Cheers
 

Reply to Cable sizes & fuse ratings . . . . in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi All Just looking for a 2nd opinion on cable sizing / breaker for a old cooker. The customer has had a 'Cooker Engineer' out to advise that...
Replies
7
Views
5K
Hi My consumer unit is located in the garage, the cables are currently clipped to a solid wall above the unit. I am considering putting the...
Replies
18
Views
6K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock