Hi
I'm installing some new floodlights and have noticed that the JB on the fitting itself will not accommodate an armoured gland but has a compression bush on it suitable for flex.
The only way I see of wiring it is to run armoured to a small JB (prob 100 x 100m) and come from there with some flex to the fitting, I can't seem to find any specific details in the regs on if there is a permissable length for the flex- or distance away from the JB the fitting can be.
Thanks
 
sounds about right. i would just make the flex as long as i have to, to give a drip loop.
 
If wiring several floodlights the use of conduit boxes is a sensible suggestion. Use a Through box with a spouted cover plate for your cable gland connection (don't forget the required cover plate rubber gaskets) for all but the last of the flood lights, where you can use a stop end box... Don't forget to use exterior rated SWA glands...

I wouldn't use black enamel boxes for exterior work, only galvanized will do... There are several means of achieving what you want to do, including using U boxes or Tee boxes instead of Through boxes. You can also go the plastic box route but in the main, they tend not to stand the test of time too well....
 

Reply to Cabling for outside flood light with PIR in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock