dgrande

I understand that the formula to work out a 3 phase current is
I= P/(1.732 * V * pf)

I have a 3 PH+N water pump rated at 4kw, so

I= 4000/ (1.732 x 400 x 0.8)

I= 4000/554.24

I= 7.21 Amps per phase

The problem I have is that the label on the pump control says that its rated current is 40Amps, Have I missed something?
thanks
 

Attachments

  • IMG_3886.jpg
    249.5 KB · Views: 130
Also lock rotor LRA I suppose but it makes no sense to me why they'd state that as a rating and not the run current and maybe the max Icu of the internal components in kA.
 
Always take notice of the electrical data label on the motor, NOT on the panel controlling the motor!! That panel could be a manufacturers standard panel, that covers many of it's pump/motor sizes etc!!
 
Last edited by a moderator:
As above always go on the name plate of the pump/motor . I have been on many a brake down in factories arguing with people who have connected a motor wrong ie- star/delta and all they will say is the last one was connected that way so I just copied connection's. Doesn't matter just refer to the nameplate for everything to do with motor you are working on that goes for connections, contactor's, overloads etc.
 

Reply to Calculating 3 phase current in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
631
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
705
wiring a 480 volt 3 phase 114 amp generator to run 2 machines. Both machine nameplate 480 v 3 phase 50 FLA. What size wire and over current...
Replies
0
Views
929
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock