How do l calculate the maximum cable length for a maximum Zs value?

Isn't there also correctional factors to be applied for ambient temperature? :confused:
 
Hi Jabbajaws

There are so many parameters when trying to work out a cable length specific to Zs max value. You need to know the circuit load, associated derating factors to allow you to select an appropriate cable from Appendix 4 of BS 7671. Then you have to work out the voltage drop taking into consideration what type of load it is for, power or lighting ? The formula Vd= mV/A/m x Ib x L and divide by 1000 will give you the actual volt drop and the figures again can be selected from Appendix 4.
You then need to know the Ze value at the incoming supply point which will allow all your calculations to be verified. To work out the Zs value you then need to work out the R1 and R2 values by using the formula:
R1= r1 ( resistance per meter from table 9A from on site guide ) x circuit length x temp correction factor (from table 9C from on site guide)
The R2 value is worked out in exactly the same manner and once you have all these results then you use the formula ZS = Ze + R1 + R2 this will allow you to see if the circuit protective device Zs value is acceptable and which will allow the safe disconnection of the circuit in the event of a fault condition.
Earth fault current is worked out from If = Uo/Zs
From these values you can work out the minimum value of the CPC for the circuit by the following:

S min = square root of the following, If squared x t ( disconnection time ) then divide by the appropriate K factor from tables 54.2 to 54.6 from BS 7671

May sound a bit confusing but there are so many factors when it comes to cable lenghts that you really have to go into minute detail to come up with the safe and correct size.

Hope this helps,

BillR3
 
Buy Amtech software the cable calc is great really easy to use, also prints off a proffesional looking report for your customers




Hi Jabbajaws

There are so many parameters when trying to work out a cable length specific to Zs max value. You need to know the circuit load, associated derating factors to allow you to select an appropriate cable from Appendix 4 of BS 7671. Then you have to work out the voltage drop taking into consideration what type of load it is for, power or lighting ? The formula Vd= mV/A/m x Ib x L and divide by 1000 will give you the actual volt drop and the figures again can be selected from Appendix 4.
You then need to know the Ze value at the incoming supply point which will allow all your calculations to be verified. To work out the Zs value you then need to work out the R1 and R2 values by using the formula:
R1= r1 ( resistance per meter from table 9A from on site guide ) x circuit length x temp correction factor (from table 9C from on site guide)
The R2 value is worked out in exactly the same manner and once you have all these results then you use the formula ZS = Ze + R1 + R2 this will allow you to see if the circuit protective device Zs value is acceptable and which will allow the safe disconnection of the circuit in the event of a fault condition.
Earth fault current is worked out from If = Uo/Zs
From these values you can work out the minimum value of the CPC for the circuit by the following:

S min = square root of the following, If squared x t ( disconnection time ) then divide by the appropriate K factor from tables 54.2 to 54.6 from BS 7671

May sound a bit confusing but there are so many factors when it comes to cable lenghts that you really have to go into minute detail to come up with the safe and correct size.

Hope this helps,

BillR3
 
Buy Amtech software the cable calc is great really easy to use, also prints off a proffesional looking report for your customers


Problem with Amtec and Hevacomp it can not use common sense when calculating cable size as if you used all the derating factors as you are suppossed to then you could end up using 16mm for a lighting circuit.:eek:
 
If it is a single phase circuit then why not use the tables in the On site guide Section 7 page 43

If you know your Ze, Protective device type, cable size and installation method then the table gives you the maximum length

If you are not sure post the above information and I will look it up for you
 

Reply to Calculating Maximum permitted cable length with maximum Zs value? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

How are you calculating maximum demand for the certificate and what should you do if your calculations exceed the main fuse rating?
Replies
9
Views
561
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
466
Hi, I am currently doing a level 2 (2365). We have been doing trunking factors and I am not sure about if you need to apply the 45% space...
Replies
3
Views
458
Calculate the temperature rise in a system consisting of six conductors carrying 1500 amperes each at 132kV, insulated with XLPE, and spanning a...
Replies
2
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock