Discuss Calculation of ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
rapier
Evening guys
When calculting ZS u us the formula ze + r1 + r2
So i have 0.18+0.60+1.00 = 1.78
But i also have my r1+r2 result which is 0.40
0.18+0.40 = 0.58
so which 1 do i use then?
Cheers guys. :)
Evening guys
0.18+0.40 = 0.58
Cheers guys. :)
So where does the 0.60 and the 1.00 come into it? I take it 0.18 is your Ze? If your (R1+R2) is 0.40 then these are added together to give 0.58 as you said. How have you come up with the other result of 1.78?
You could measure it aswell
then that is zs
ze= 0.18
r1= 0.60
r2 = 1.00
so zs = ze + r1+r2 zs = 0.18+0.60+1.0 = 1.78
you are using r1+r2/4 value which is the outlet expected readings which is 0.60 + 1.0 / 4 = 0.40
So 1.78 is the answer.
what are u tryin to say about the last bit sorry mate.
So what happens if u have a lighting circuit, u dont have your r1 + r2 measurements as you wouldnt find these readings as its not on a ring.
But u would just get ur (R1+R2) by joining the live and earth together. So how would u find the measurement of zs by calculating.
you join live to earth at the board and go to the last light and take the reading across live earth and hey presto r1+r2
for the ring were you testing opposite live and earth together or testing the live and the earth and adding them together
link line and cpc at db reading at last outlet is r1+r2
or to calculate add yor ze to tabluated figures for resistence of cable from onsite guide table 9a page 166
example a 2.5/1.5 cable has a resis of 19.51 ohms per metre so for say 15 metres:
19.51 x15 /1000 = a r1+r2 of 0.29 ohms
There are other factors, ambient temp, max op temp to take into account. Please buy GN3. It looks really boring and can be but it's full of interesting stuff (unlike some of us!!)
I think you (and maybe a few others) are getting a little confused here.
Zs=Ze + (R1+R2) NOT Zs=Ze + (r1 + r2).
As you have said, the latter only applies to RFC's.
Hi all
common everbody
ZS=Ze+(R1+R2) then mulitplied by the correction factor for max operating temperature of the cable
onsite guide table 9c
page 168
cheers
Rapier is confusing his r1+r2 with R1+R2.
He should also know that R1+R2=(r1+r2)/4 for a ring.
Have a look at the OSG under testing, esp page 82.
And make damn sure you take out the neutral out at the CU (and earth it) too else you might get a little bit of a surprise , especially if you have flourescents on the lighting circuit! :eek:
hi there
Jason i agree with you but you ALL MUST CONSIDER maximum ZS no one here has mentioned this !!!
It is not what zS is
it is what value is used for ie to make sure that the protective device operates within the correct disconnection time
Does the zs value EXCEED that of the values given in tables 41.1 to 41.5 etc of the regulations
then it is not a safe circuit etc
hope this helps a bit
cheers all
hI Guys,
Interesting listening to our conversation as i am just learning myself and trying to get my head around testing .
When ou do the testing on a lighting circuit and you have to take your R1 and R2 reading at the last ceiling rose , is this because the resistance there should be at it highest?.
Secondandly, once you have taken that reading, do you have to test at every switch and ceiling rose after, that if so , where would you put your leads in the two way , and the intermidiate switch as there are three and four points .
As i remember from test board at college we did R1and R2 reading at rose , flicked switches for polarity, then we had to go in each switch as well , this is what im confused about , was this for continuity between earth and live.
Ive loads to ask as iam confused ,
Thanks for your patience,
Snowplough
Hi guys am I right in saying that if the circuit in question is protected by rcd/rcbo then there is no need for the multiplier. (table 41.5) really unsure about this. Any help would be good I've got my 2394 written tomorrow I've pasted the practical and multiple choice.
Not sure what you mean.
If you mean the 0.8 correction factor for the temperature, it would hardly apply to 1,666Ω - would 1,333Ω be satisfactory for a circuit?
If you mean an RCD/RCBO means you can ignore the maximum Zs for the overcurrent protection device then - no, you are not right.
No I know you still have to check zs readings with those set in bs7671 I know that rot is 80% of regs readings. I'm talking about if cables are bunched or if temp is not 20degrees sorry for being unclear but iPhones and long explanations are a real bad mix
So is digging up threads that are 4+ years old!!
Reply to Calculation of ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...