Morning all,
Just after a bit of knowledge!!
Been to a job to move a light switch. When I got there noticed a callender main cut out . The incoming cable is enclosed in conduit and main earth has been bonded to that. The conduit looks like it goes straight through wall into next door as it is a row of 4 cottages. Did Zs and got 13ohms. Had a look for earth stake but have not seen anything.
is this system not uncommon in previous yrs. it looks like house has had new db and some new circuits fitted fairly recently as it has a split load board and new cable colour.
Any advice would be greatly appreciated and I have tried to post a photo.
ThanksC5D9250D-C1BF-4425-85A9-F991BF0E4F18.jpeg
 
Last edited by a moderator:
Without accessing the other side it is difficult to say, the earth may just be earthing the conduit and not providing an earth as such plus it looks quite recent.
 
Earth via conduit is not uncommon and can be perfectly satisfactory, but as mentioned above one cannot assume that every conduit is properly earthed at source. The ring terminal under one of the cover screws of the inspection elbow is not correct practice and suggests an afterthought, i.e. that was not supposed to be the means of earthing.

I would not be surprised to find that the conduit is not connected to the supply earth where the shared service splits, and the installation is getting its earth via the bonding.
 

Reply to Callender main cut out and main earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
280
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
277
Hi all, After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth. I...
Replies
6
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock