Discuss Campsite Electric Hook-up connection in the Australia area at ElectriciansForums.net

D

dunny1234

Looking at a job on a farm campsite. They require hookup's for 18 touring caravans in a field thats 85m long (9 caravans up one side, and then 9 caravans down the other) . An approx. calculation is that i need 250m of 16mm swa cable. I'm looking at using 16a 2way hookup unit/rcbo's for every 2 caravans. Not done anything like this before, any advice would be great. Do you think 16mm swa is enough. Thanks
 
assuming a 10A supply for each caravan that's 90A without diversity. 10mm XLPE SWA is rated at 81A ( AEI Cable Finder Wizard ) so should be sufficient ( and a hell of a lot easier to install). volt drop could be an issue here though.
 
Last edited:
Thanks teletrix. I suppose 10mm swa would be cheaper too, the farmer would like that. But, volt drop over 250 metres is a concern. I told the farmer roughly what 16mm swa would cost and he seemed okay. Might as well be safe. What do you reckon? Thanks again
 
are you doing it in 1 run or 2? i would either run 2 radials, 9 vans each, or make a ring.
 
I reckon you should do the calc's required for this installation, especially those regarding ''volt drop''

The farmers incoming supply is almost certainly going to be PME/TNC-S, so it's gong to have to be TT systems. Maybe linking them all up on each line of caravan pitches will give you decent Ra values that you can work with....
 
I reckon you should do the calc's required for this installation, especially those regarding ''volt drop''

The farmers incoming supply is almost certainly going to be PME/TNC-S, so it's gong to have to be TT systems. Maybe linking them all up on each line of caravan pitches will give you decent Ra values that you can work with....
i,m just wondering how to calc. volt drop on an install like this. assuming 1 or 2 radial circuits, the load is taken at varying points, i.e. the load at the end of a run is not the total load. (only 10A if each van has a 10A supply) so would you use 10A for the full cable length, and calculate say at 50% of the length at say 30A ( allowing na bit of diversity)
 
I recently did a similar job although in a boating marina, its amazing the distance and volt drop. We allowed about 8 -10 amps per boat over 230 mtrs and ended up putting 25mm in. Our incomer was a TN-S system but due to the distances and the fact the hook up posts each had RCD built in we TT'd every post and also we protected the SWA with a 300ma time delay RCD
 
Remember, if direct burial the correct trench depths, and correct materials are used for back filling. DON'T let the farmer back-fill with just the excavated earth from the trenches!!! Better to duct the cables, but then costs go up!!
 
I'm struggling with how much diversity / calcs on this cable design. Taking full whack (which isn't going to happen) 18 x 16A = 288A and cable size for that is 95mm2 plus! The farmers going to have a heart attack when i tell him how much thats going to cost. surely thats not right
 
i,m just wondering how to calc. volt drop on an install like this. assuming 1 or 2 radial circuits, the load is taken at varying points, i.e. the load at the end of a run is not the total load. (only 10A if each van has a 10A supply) so would you use 10A for the full cable length, and calculate say at 50% of the length at say 30A ( allowing na bit of diversity)


On a radial circuit, your biggest loading is at the first point, 9 x caravans at 10a =90A. Second Point 8 x 10A =80A , and so on. To conduct a diversity exercise you will need some experience of such caravan installations, which i'm sorry to say i don't have. Maybe someone here on the forum, will be able to help on that score for you....

The volt drop calculation is similar to those or a row of lights so distance x load at each point along the circuit then combine the totals
 
Last edited by a moderator:
as a rule of thumb, i would apply 50% diversity, as i can't imagine average load for 9 caravans > 5A average at any one time. that's mt guesstimate. someone might prove me wrong. it's something i've not come across before, except one site where 4 caravan pitches were taken from the car park lighting which was on a 10A MCB. he wanted me to sort out the"nuisance tripping" of the MCB. FFS.
 
The farmer will have loads of rolls of the ducting needed to bury the cable in, so wont need to buy more, its something pretty much all farmers keep a large stock of, and he will probably have his own digger as well, so he will be able to sort out any trenches that need digging....
 
Just wondering doesn't each socket outlet at the caravan pitch need individual overcurrent protection? so would not be able to do it in a ring or radial?
 
Just wondering doesn't each socket outlet at the caravan pitch need individual overcurrent protection? so would not be able to do it in a ring or radial?

Correct me if ime wrong but I thought the discussion was ring or radials feeding a rcd,mcb connection points to each pitch with maybe metering included? That's what I thought would be required? Although as you say hasn't been mentioned.
 
Just wondering doesn't each socket outlet at the caravan pitch need individual overcurrent protection? so would not be able to do it in a ring or radial?

How do you know if these Caravan supply units don't incorporate an MCB, as well as the RCD?? Personally i don't know, but i would assume that they will!!! Maybe a DP RCBO even....lol!!!
 
Last edited by a moderator:
Just checked over the regs i think i read it wrong i thought it meant each socket had to be on a seperate circuit/cable. my bad lol.
 
I would like some bright spark to explain the volt drop equation for me in this circumstance, basicly if each point is rcd,mcb etc protected then isn't it just a bunch of sub mains connected together?
 

Reply to Campsite Electric Hook-up connection in the Australia area at ElectriciansForums.net

Similar Threads

I have a small caravan park with 8 pitches. Each have a Rolec Electrical Hook-Up unit fitted with a Rolec 16A Single Pole and Neutral 2 Module C...
Replies
14
Views
2K
I'm sure this will have been covered before but please bear with me. Have been asked to replace a main Distribution board for a fairly small...
Replies
23
Views
5K
Bought a house a few months ago and would like to have access to electrical outlets in the garage. There is already an electric cable running to...
Replies
21
Views
2K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
545
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock