saabuldin
Can anyone recommend a link or website where i can find short circuit capacity table for type C MCB's
Discuss Can anyone recommend a link or website where i can find short circuit capacity table in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
hi mate gn3
shows a table for all fuses and CBs for ics value and icn value it depends as pevvers says whats the BS number
ie bs3036 are between 1 - 4 kA
bs1361 type 1 16.5kA
bs1361 type 2 33 kA
bs 88-2-1 50kA at 415v
bs 88-6 16.5 at 240v
& 80 at 415v
CBs to bs 3781 will have m1 which is 1kA
M 1.5 1.5kA
M 3 3 kA
M4.5 4.5 kA
M6 6kA
M9 9kA
bsen 60898 and rcbos between 1.5 and 25 kA
yea mate i forgot to put that it should state on the device the bs number and icn value the table is in Gn3That's a very good reference indeed, but unless the OP actually looks at the device, which is a type C, I assume 60898, then it could be anything!!
3, 6, 10 even maybe 16kA...
Reply to Can anyone recommend a link or website where i can find short circuit capacity table in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net