There is a double socket on the wall where the main feed comes in and this is then connected to a none switch fused socket. Iv'e been told i can add a other fused switched socket and connect both together then run 2 additional sockets off the fused switch one?
 

Spoon

Mentor
Electrician's Arms
Trainee Access
Messages
7,886
Location
Lancashire
Welcome to the forum mate.
What do you mean by a "none switched fused socket"? Do you mean one of these?
upload_2019-2-10_9-18-55.png
Does the circuit you are adding to have RCD protection?
Does the way you intend to add the extra sockets need the wires to have RCD protection?
We need more info mate.
 

l4urence

Regular EF Member
Messages
185
Location
East Sussex
Note @Spoon comments. The non-switched 'fused socket' is confusing the question unless it looks like the item pictured.
 

l4urence

Regular EF Member
Messages
185
Location
East Sussex
I'm looking again at the original question.
why would you want to add another fused connection after the first?
so:
ring socket <---xFCUx---xSKTx---xSKTx
if those sockets take more than the first 13A fuse they will stop (fuse blows).
so:
ring socket <---xFCUx---xSKTx---xSKTx--xFCUx---xSKTx
makes no sense - the same would happen. The first FCU protects the connected sockets.

That said. You need to look at what loads you are expecting to connect and where they are positioned on the ring. By design a leg on the ring (the cable between sockets) the Iz shouldn't go above 20A. If you are adding these sockets to either end of the ring, those closest to the CU - you could well do that. You need to calculate the leg length impedances for the final ring and calculate the expected current going both ways (parallel circuit). Someone qualified and with the correct test equipment can calculate these for you to make sure this would comply.
 

Spoon

Mentor
Electrician's Arms
Trainee Access
Messages
7,886
Location
Lancashire
I think I scared the OP off, by asking questions..
 

Moley

Baaaa!!!
Messages
316
Location
Pontypridd, S.Wales
He posted at 4:56 am. Maybe posted before work or after night shift? So either he's just due home or just getting up?? I didn't even realise that time existed on a Sunday.
 