Hello! I’m confused as to how to add up total amperage on my panel when it comes to double pole and single pole. So I can avoid overload. I want to add a 50 amp breaker. Any advice?90A20AF0-4B21-47A4-B9EE-6B2B843179B1.jpeg
 
Last edited by a moderator:
Hello! I’m confused as to how to add up total amperage on my panel when it comes to double pole and single pole. So I can avoid overload. I want to add a 50 amp breaker. Any advice?View attachment 58590
Stevey I’m sorry to tell you this but your panel is full with no extra space left. If you will hire an electrician he or she could possibly add slim line breakers in your panel to free up some space to add another breaker. Don’t worry about overloading your panel. I had to do them same thing last weekend
 
Doubt you will overload that panel- most residential services are over-sized even by NEC load calc standards. If any space will take a quad breaker I'd go that route. Make sure you use Siemens/Murray, I see a Cutler Hammer BR breaker to the top left which is technically not for that panel.
 
Doubt you will overload that panel- most residential services are over-sized even by NEC load calc standards. If any space will take a quad breaker I'd go that route. Make sure you use Siemens/Murray, I see a Cutler Hammer BR breaker to the top left which is technically not for that panel.
Stevey what is that 30 amp double pole breaker on the top right that is turned off used for. If it’s not being used it can be taken out and install the correct 50 amp breaker in that space
 
Stevey I’m sorry to tell you this but your panel is full with no extra space left. If you will hire an electrician he or she could possibly add slim line breakers in your panel to free up some space to add another breaker. Don’t worry about overloading your panel. I had to do them same thing last weekend
There is a spot for a double pole at the bottom left. Sorry the angle was bad.
[automerge]1591224204[/automerge]
Doubt you will overload that panel- most residential services are over-sized even by NEC load calc standards. If any space will take a quad breaker I'd go that route. Make sure you use Siemens/Murray, I see a Cutler Hammer BR breaker to the top left which is technically not for that panel.

Quad breaker? This is my first time hearing big of this.. what would be the benefits for this?
[automerge]1591224275[/automerge]
Stevey what is that 30 amp double pole breaker on the top right that is turned off used for. If it’s not being used it can be taken out and install the correct 50 amp breaker in that space
Hello! I need the 30 amp it is for my dryer ?
[automerge]1591224714[/automerge]
My concern is that I was told to only run at 80% capacity on a breaker. If I were to install another 50 amp I know this would be the draw. At the least. I have an indoor hydroponic setup and they require a lot of power. Three separate rooms. 3 of the rooms drawing 15 amps each for the regular 120 volt sockets, a mini split drawing 30 amps in both rooms and then 50 amps each to power the equipment consistently for 12 hours. The other third room drawing 30 amps. Totaling to about 190 in double pole amperage. And 45 in single pole.

I have yet to add in the draw for the office space(15 amps), stove + kitchen circuit, water heater.

also what is the facts about using a different branded breaker? Is this a big issue?
 
Last edited:
There is a spot for a double pole at the bottom left. Sorry the angle was bad.
[automerge]1591224204[/automerge]


Quad breaker? This is my first time hearing big of this.. what would be the benefits for this?
[automerge]1591224275[/automerge]

Hello! I need the 30 amp it is for my dryer ?
[automerge]1591224714[/automerge]
My concern is that I was told to only run at 80% capacity on a breaker. If I were to install another 50 amp I know this would be the draw. At the least. I have an indoor hydroponic setup and they require a lot of power. Three separate rooms. 3 of the rooms drawing 15 amps each for the regular 120 volt sockets, a mini split drawing 30 amps in both rooms and then 50 amps each to power the equipment consistently for 12 hours. The other third room drawing 30 amps. Totaling to about 190 in double pole amperage. And 45 in single pole.

I have yet to add in the draw for the office space(15 amps), stove + kitchen circuit, water heater.

also what is the facts about using a different branded breaker? Is this a big issue?
There is a spot for a double pole at the bottom left. Sorry the angle was bad.
[automerge]1591224204[/automerge]


Quad breaker? This is my first time hearing big of this.. what would be the benefits for this?
[automerge]1591224275[/automerge]

Hello! I need the 30 amp it is for my dryer ?
[automerge]1591224714[/automerge]
My concern is that I was told to only run at 80% capacity on a breaker. If I were to install another 50 amp I know this would be the draw. At the least. I have an indoor hydroponic setup and they require a lot of power. Three separate rooms. 3 of the rooms drawing 15 amps each for the regular 120 volt sockets, a mini split drawing 30 amps in both rooms and then 50 amps each to power the equipment consistently for 12 hours. The other third room drawing 30 amps. Totaling to about 190 in double pole amperage. And 45 in single pole.

I have yet to add in the draw for the office space(15 amps), stove + kitchen circuit, water heater.

also what is the facts about using a different branded breaker? Is this a big issue?
Stevey what is that 30 amp double pole breaker on the top right that is turned off used for. If it’s not being used it can be taken out and install the correct 50 amp breaker in that space
Stevey you can’t add all your breakers. What is meant by quad is slim line breakers. Regular breakers are 1 inch and slim line breakers are 1/2 inch so you can install 2 for one. Quit worrying about overloading your panel if you add all the breakers it will certainly be over 200 amps but if you would put an amp probe on your panel you probably are not going to pull over 60 amps at the most. I’ll explain it like this you have what’s called a calculated load which is what you see on your breakers then you have a connected load. With that said that you will not be having all breakers pulling amperage like your hot water heater, oven, dryer, heat, air conditioner, microwave will not be pulling amperage on all breakers at the same time. I hope you understand what I just told you and quit worrying
Hello! I’m confused as to how to add up total amperage on my panel when it comes to double pole and single pole. So I can avoid overload. I want to add a 50 amp breaker
[automerge]1591228941[/automerge]
There is a spot for a double pole at the bottom left. Sorry the angle was bad.
[automerge]1591224204[/automerge]


Quad breaker? This is my first time hearing big of this.. what would be the benefits for this?
[automerge]1591224275[/automerge]

Hello! I need the 30 amp it is for my dryer ?
[automerge]1591224714[/automerge]
My concern is that I was told to only run at 80% capacity on a breaker. If I were to install another 50 amp I know this would be the draw. At the least. I have an indoor hydroponic setup and they require a lot of power. Three separate rooms. 3 of the rooms drawing 15 amps each for the regular 120 volt sockets, a mini split drawing 30 amps in both rooms and then 50 amps each to power the equipment consistently for 12 hours. The other third room drawing 30 amps. Totaling to about 190 in double pole amperage. And 45 in single pole.

I have yet to add in the draw for the office space(15 amps), stove + kitchen circuit, water heater.

also what is the facts about using a different branded breaker? Is this a big issue?
Stevey no matter what name brand panel you have look under the cover at the factory sticker. It has the style and type breakers you can use plus the torque requirements. A lot of different name brand breakers will work but if an inspector sees that that particular breaker is not recommended he or she will fail your installation and will not let you have power until it is corrected.
[automerge]1591229012[/automerge]
There is a spot for a double pole at the bottom left. Sorry the angle was bad.
[automerge]1591224204[/automerge]


Quad breaker? This is my first time hearing big of this.. what would be the benefits for this?
[automerge]1591224275[/automerge]

Hello! I need the 30 amp it is for my dryer ?
[automerge]1591224714[/automerge]
My concern is that I was told to only run at 80% capacity on a breaker. If I were to install another 50 amp I know this would be the draw. At the least. I have an indoor hydroponic setup and they require a lot of power. Three separate rooms. 3 of the rooms drawing 15 amps each for the regular 120 volt sockets, a mini split drawing 30 amps in both rooms and then 50 amps each to power the equipment consistently for 12 hours. The other third room drawing 30 amps. Totaling to about 190 in double pole amperage. And 45 in single pole.

I have yet to add in the draw for the office space(15 amps), stove + kitchen circuit, water heater.

also what is the facts about using a different branded breaker? Is this a big issue?
Stevey no matter what name brand panel you have look under the cover at the factory sticker. It has the style and type breakers you can use plus the torque requirements. A lot of different name brand breakers will work but if an inspector sees that that particular breaker is not recommended he or she will fail your installation and will not let you have power until it is corrected.
 
Last edited:
It will work, I see no reason why you can't add a 30 amp breaker to the panel. Adding the handle rating of each breaker means nothing, not everything will run at once, at full current draw. I'm willing to bet you could get away with a 60 amp main breaker.
 
Stevey you can’t add all your breakers. What is meant by quad is slim line breakers. Regular breakers are 1 inch and slim line breakers are 1/2 inch so you can install 2 for one. Quit worrying about overloading your panel if you add all the breakers it will certainly be over 200 amps but if you would put an amp probe on your panel you probably are not going to pull over 60 amps at the most. I’ll explain it like this you have what’s called a calculated load which is what you see on your breakers then you have a connected load. With that said that you will not be having all breakers pulling amperage like your hot water heater, oven, dryer, heat, air conditioner, microwave will not be pulling amperage on all breakers at the same time. I hope you understand what I just told you and quit worrying

[automerge]1591228941[/automerge]

Stevey no matter what name brand panel you have look under the cover at the factory sticker. It has the style and type breakers you can use plus the torque requirements. A lot of different name brand breakers will work but if an inspector sees that that particular breaker is not recommended he or she will fail your installation and will not let you have power until it is corrected.
[automerge]1591229012[/automerge]

Stevey no matter what name brand panel you have look under the cover at the factory sticker. It has the style and type breakers you can use plus the torque requirements. A lot of different name brand breakers will work but if an inspector sees that that particular breaker is not recommended he or she will fail your installation and will not let you have power until it is corrected.
Thank you very much!! God bless you. ?
 

Reply to Can I safely add a 50 amp breaker to this? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

OK to add a 50 Amp breaker in this panel for a 220V EV Charger? Maybe swap some single 20 Amp breakers for dual 20 amp breakers? Can I add a 50...
Replies
2
Views
588
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
800
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
687
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
267
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
560

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock