Interesting, i understand how a shower works but surely the element has to work harder to heat colder water same as a kettle as thats all a shower is just alot bigger version. If you have really cold water your kettle takes longer to boil.

The question to answer further above was does an electric shower run on full load constantly??

I dont believe it does because of the factors listed above.

What do you think??
Shower runs on half/full load constantly as well

It'll change temperature if flow changes or may even cut out
 
Mine (mira Sport) cuts out at 48C if flow of water too low, it also has a non resettable hi limit stat that cuts out the power permanently at a much higher temperature, these two stats are combined in one which is known as a TCO.
 
Should also have added that you will hear the TCO clicking off approx 15 secs or so after switching off the shower as there is alot of residual element(s) heat still present when the flow of water ceases.
Some showers also have a phased shutdown where the elements power is switched off ~ 10 secs before the water is shut off, its claimed that this helps to prevent limescale build up on the elements in hard water areas.
 
I love these convos you have to put every detail in about every product or operation. The science behind it or the physics, the calculations like you designing an electrical installation right from your phone.

If you put anything in laymans terms someone is quick to point out a fall or bite ?

Have fun guys another forum i wont be on again.

You lot are way better electricians...well done
 
I love these convos you have to put every detail in about every product or operation. The science behind it or the physics, the calculations like you designing an electrical installation right from your phone.

If you put anything in laymans terms someone is quick to point out a fall or bite ?

Have fun guys another forum i wont be on again.

You lot are way better electricians...well done

You been on something? This forum is a good mix of banter and good knowledge. If you have problems on here then god help you in society.

Stick around, you'll get used to us ?
 
Why the dislike Pete? Hope I haven't said something wrong.
 
A heating element takes the same power to heat up…. Be that a 2.5kW kettle or a 9kW shower…. Whether it’s cold or warm water going in, it’s stil 2.5 or 9 to heat it.
As before, it’s how much water. Either stored water, like a kettle. The less water, the quicker it takes to boil…. Or a shower, the faster the rate of water passing through.

An element is a constant resistance…. Supply voltage is constant…. So the power taken by the element is constant.
(Give or take a little change of resistance as it heats up)
 
agreed. a 3 kW kettle takes 2 minutes to boil. a 2kW kettle takes 3 minutes ( for the same amount of water). which costs more?
 
Based on a 240V, 7.5kw shower and a total length of 16M of 4MM2 cable and assuming cable resistance at 4.3mohm/M then my (rusty) calcs give a current flow of 30.975ohms and a shower output of 7.368kw and a voltage drop of 2.13V through the cable resulting in a cable heat loss of 65.94watts or 4.12watts/meter of cable.

So is 4MM2 suitable??.
 
suitable, but not ideal, esp if there's the possibility of insulation being added by the itchy-poo monkeys.
 
I agree a 100 per cent that the main reason a shower switch burns out is down to a loose terminal connection or cheap shower switch especially where we as sparks are cramming a 10mm cable into a 47mm pattress on the wall loosing them in the process.

However from my experience if your over-rate your cable from say a 9.5kw shower on a 6mm cable it can cause heat to dissipate anywhere on the cable. So where theres a big box on the wall full of single insulated cables with no heat to escape you see it travel all up the cable.

Some ive seen so bad the the whole cable has had to be replace. Simarily to where the cable has been bent or weakened through installation. Heat is going to affect the cable where it is most weak first so at joins or switches.

Still it takes a long time for a 9kw shower to cause the cable to burn up as its never running at full load most of the time.
Somebody recently wanted me to fit a shower switch shed bought from wickes...
It felt light, looked shyte and came complete with a 27mm surface box to mount it on...

I took one look at it and said: "nah....yer allrite love"

Went round the corner and got a decent one weighing twice as much and a 47mm box...

I don't know why people persist in going to these diy stores for electrical stuff...?
 
Somebody recently wanted me to fit a shower switch shed bought from wickes...
It felt light, looked shyte and came complete with a 27mm surface box to mount it on...

I took one look at it and said: "nah....yer allrite love"

Went round the corner and got a decent one weighing twice as much and a 47mm box...

I don't know why people persist in going to these diy stores for electrical stuff...?
coz they know no better. i will only fit the crabtree or click 50A round jobbies. them square ones suck.
 

Reply to Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
511
Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K
Seen a couple of videos with Doncaster cables now producuing a T&E with the CPC already sleeved so no need to fit our own. I also read somewhere...
Replies
19
Views
638
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
530
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
382

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock