thekingiam

i have 25 mm swa suplying cu in top flat, i want to put in 80amp type s 30ma rcd to protect cable and time delay.
problem i have is cable route is onto existing ceiling which will be lowered and pipe work in way to rcd so i was thinking of connecting to henley blocks in ceiling then down to rcd is this allowed?
while typing this out i thought i don't need henley blocks as i could put a back box in ceiling connected to armour and just peel back armour so no need to terminate if that makes sense?
 
Maintenance free joint if not accessible.
 
Hi
I think you have 2 problems here.
1. A hidden connection box with screw terminals.
2. Availability of 30mA S type rcd. 100mA is no problem!

Pete
 
my last point was as you would connect armour of cable to a metal box before entering a cu , i can do this in ceiling void as i am not cutting into lives and seperate earth ie 3 core.
i would imagine i need a connection to earth from metal box to protect armour?
maintanance free ?would it have to be as only a swa armour connection?
have 80 amp 30 ma s type rcd going to feed a lower rated rcd so lower rated rcd trips first
 
my last point was as you would connect armour of cable to a metal box before entering a cu , i can do this in ceiling void as i am not cutting into lives and seperate earth ie 3 core.
i would imagine i need a connection to earth from metal box to protect armour?
maintanance free ?would it have to be as only a swa armour connection?
have 80 amp 30 ma s type rcd going to feed a lower rated rcd so lower rated rcd trips first

I don't fully understand what your thinking is. If cables are connected together in the ceiling void with no marked access the connection has to be Maintenance Free and this includes earth conductors. If you are an electrician you'll Know what this means - no screw connections - only crimp, solder and clamp units designated MF are ok.

RCD. a. Why do you need one? b. You cannot follow a 30mA S Type with a 30mA, apart from which I don't think you can buy one anyway.

Pete
 
main incommer from meter goes to isolator then into henley block on distrubution board then split from henley to cu's on the board,the new supply to top flat will come from this henley to rcd on board then swa tails into ceiling metal box then on to top flat cu.
does this make better sense ?
 
the rcd protects the length of swa against drilling etc, also time delayed so top flat rcd trips before the time delayed one, the metal box in ceiling will have a blank plate flush with ceiling so access is no problem for inspection.
 
it's my own house so not realy needed but as i would of put an isolator in anyway 20 quid for rcd doesn't seem to much effort.
edit missus house she would kill me if she heard me calling it mine!
 
main incommer from meter goes to isolator then into henley block on distrubution board then split from henley to cu's on the board,the new supply to top flat will come from this henley to rcd on board then swa tails into ceiling metal box then on to top flat cu.
does this make better sense ?

What's the overcurrent protection for the new SWA submain?
 

Reply to can i use henley blocks in ceiling? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In the UK, It is said that the neutral wire is connected to ground/earth wire along the way back to the substation. Ive inherited a setup where...
Replies
4
Views
1K
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
So as the title says can I use a mcb as the main switch. Basically to keep it short I’ve took a 25mm sub main to power an outbuilding. Mains...
Replies
11
Views
3K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock