cyberjunction
Hi
In relation to my earlier post, http://www.electriciansforums.net/e...1-please-help-crabtree-starbreaker-board.html
Can some one please clarify for me? Cutting a long story short, I am new to this but fitted 20m of 6mm in plastic conduit externally for a shower, reference method B???
If I am reading it correctly Table 7.1, OSG page 50 , 40Amp Can only be installed by Method C and NOT B. Does This mean I have totally ballsed it up? Surely 6mm calble is allowed in conduit.
Also table 7.2 OSG page 52 tells me Ref B 6mm is max 38A but table 6D1 OSG page 128 says 41A. Shower is 8500w so am just in but wanted to learn why.
Sorry if I am being thick but its my first job and I am stressing !!! I passed Elecsa assesment but have not done much since.
Thanks in advance