Hi Everyone,
I'm just hoping someone has had this problem and found a way to get over it.
I do work for water feature companies, yesterday I came across an awkward problem, they'd installed maybe 70m of 2.5 3 core SWA, down to a pond to run a pump and UV light, load total 7A.
The idea was to spur off a DSSO in the main house via an RCD spur and provide two outlets by the pond for the pump and UV.
Pretty straightforward !!
All connected, power up and RCD will not stay in, sometimes tripping the main house RCD, I know two 30mA trips in line is not ideal but it was specified. So OK I think I've made a mistake, take it apart piece by piece and check, using the insulation tester as I go.
I finally am back where I started with every end open and everything showing as close to infinity as makes no difference. I spent ten years of my career on T&R contracts with a meter in my hand all day so I'm reasonably confident with it, but this had me checking and rechecking, but the figures remained the same for cable and appliances.
All put back together the pump and light will run all the time the earth of the SWA and Sheath are not connected, as soon as they are it will trip the RCD spur as if the is a fault, but the meter will show none at 500v.
It can only be capacitive inductance, the system needs an earth as it's a buried SWA and the pump and UV need to be protected for users safety obviously.
This leaves us in an awkward situation as the cable has been buried and landscaped over some time ago, but the feature has to work.
Has anyone come across the problem of capacitive inductance and found a safe and effective way round it.
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

mhar

-
Arms
Well, if it isn''t the cable it will be whatever is on the end of it such as a pump with high earth leakage. Can you PA test it with a decent tester to determine the amount of leakage?
 
  • Thread Starter Thread Starter
  • #3
No, as I said everything tests clear, this is why I can only think it is capacitive inductance, so I was wondering if anyone had any ideas of something that can be added to diffuse the inducted voltage.
It is to do with the SWA as we've had the whole thing running on a couple of 50m extensions plugged into an RCD.
It's just a strange set of circumstances.
Thanks for getting back so quick though
 

Wilko

-
Arms
Esteemed
Hi - apologies, I know you’ve said you’ve tested the cable and it passes, but it sounds like it’s N-E damaged. Any joints in the run? Can you power everything up with no loads connected at the far end?
 
  • Thread Starter Thread Starter
  • #5
Hi,
No joints, they've assured me the cable was laid by hand not machine so hasn't been damaged in that way.
I'm not being arrogant but as I said I spent years fault finding etc and this has completely thrown me.
The cable with the two D.P isolators switched off when livened up will knock out the RCD in about two seconds.
Several times I've disconnected the end and tested the cable at 500v and it'll show 200+ core to core brown to black and grey and with say grey to black then brown and black, the sheath is clear to all cores.
Honestly, I didn't give up easily as I only priced for a day and it's an hour away, but I can only put it down to some kind of inductance.
By the way I'm 55 and been doing this too long and this is only the second time I've come across anything like this
 

mhar

-
Arms
Test the swa at 1000V?
Have you tried only using two cores and use the armour as cpc?
 

ipf

-
Mentor
Arms
Esteemed
'Capacitive inductance' is a new one to me.
Are we talking reactance......be it inductive or capacitive?
 
UV light does damage stuff . (can it be left out of circuit to rule it out )..
( Is it an old fashioned fluorescent ... Inductive starting spike ? )
IR only going bad when it actually .
a) Is lit
b) IS striking to light.
c) Grumpy tube flickering its ass off/damaging balast
 
What a fascinating (and frustrating!) problem! Is the supply TN-C-S or TN-S? 70m is a long run of cable and I wonder if, assuming at the far end there is some connection to the earth (pump casing, SWA terminated in steel box screwed to concrete etc), there is a differing earth potential between the house and the pond? This may upset the RCDs in some way?

You said that you'd powered it up with two extension leads and it went OK, but without wishing to be rude, did you ascertain that there was actually an earth present at the pond end extension lead? Extension leads take a bashing and it's not unknown for cores to become disconnected.

Another thought was have you checked end to end resistance of each core of the SWA in case it's some obscure cable manufacturing fault. Also it's not unknown for colours to change along a run of cable if they put the wrong coloured PVC in the machine at the factory. Highly unlikely but I had it when I was PAT testing a mains lead once.

Hope you get it sorted soon!
 

Lucien Nunes

-
Mentor
Arms
Esteemed
The OP says the IR is all good and suspects that the tripping is caused by capacitive leakage. As per ipf, capacitance and inductance are different - sort of opposites - and what you are talking about is capacitive susceptance (the reciprocal of reactance, as admittance is to impedance and conductance is to resistance).

The capacitance in question is from the line core to the combined earthed parts, i.e. the earth core (as it's 3-core) and the armour. The capacitance to the neutral core doesn't contribute earth leakage as the current returns to neutral. From the link below I get a figure of 0.25μF /km for the star capacitance of 3-core 2.5mm² BS5467 SWA. Theoretically we have to exclude the neutral core, but it's the only figure I can find. You reckon it's 70m long.

C=0.25/1000*70=17.5nF
Xc= 1/2.pi.f.C =181kΩ
IΔn=230/181k=1.3mA approx.

So you are right to consider that capacitive leakage can contribute measurably to the total, but in this case it's nowhere near causing the RCD to trip on its own. Even if our figure for capacitance is out by a factor of 5, it still can't be the sole cause of a minimum 15mA leak at 230V.
 

plugsandsparks

-
Arms
Esteemed
I would be looking for cable damage, try another tester and suspect damp, as from my experience damp can be a real pain when it wants to and only respond to a a/c waveform, dont understand how or why but i have had happen to me.
 
  • Thread Starter Thread Starter
  • #15
Thank you to everyone for your replies, between you all it has given me a more balanced perspective on the problem.
I'm due back there next week to hopefully complete things.
I will start with a thorough testing of everything, as we all know there shouldn't be any great mystery to 70m of 2.5 SWA running a couple of spurs to a UV and pump. I'm sure I already have but !!!
What didn't help, was the fact that the house belongs to someone famous and at lunchtime they had a number of guests for dinner, being part of the garden scenery and twice being responsible for knocking out the downstairs power and the CU being in the same room as events, may have upped the ante and made it a little more tricky to keep a logical frame of mind, for testing and fault finding.
Everyone is very nice about things, but we could all do without it !
I'll post the results, in case anyones still interested.
 

stevethesparks

-
Arms
Esteemed
You say you have two RCD's (in-series) is it the same RCD that trips every-time or both?
If just the one, have you tried replacing the RCD?
In my experience, a ramp test does not always identify a faulty RCD.
 
  • Thread Starter Thread Starter
  • #18
PS I think Grommit you may be onto something with the different earth potentials, one of the things I'm taking with me is a stake and once I've checked for all other faults, I had thought just to take L+N from the house, use two RCD spurs and they can run as a TT system down by the pool.
Lucien seems to have written out the capacitance idea, grabbing at straws really, so two different potentials does seem the most logical way to look at it.
 
  • Thread Starter Thread Starter
  • #19
PS I think Grommit you may be onto something with the different earth potentials, one of the things I'm taking with me is a stake and once I've checked for all other faults, I had thought just to take L+N from the house, use two RCD spurs and they can run as a TT system down by the pool.
Lucien seems to have written out the capacitance idea, grabbing at straws really, so two different potentials does seem the most logical way to look at it.
 

telectrix

-
Mentor
Arms
Esteemed
start off by removing the RCD FCU. or supply from a non-RCD way in the house CU. still tripping? got to be the SWA. as previous post, a fault may not show up on a D.C., low current IR test, but bites your arse when you stick a higher current capable A.C. voltage.
 
O

Octopus

PS I think Grommit you may be onto something with the different earth potentials, one of the things I'm taking with me is a stake and once I've checked for all other faults, I had thought just to take L+N from the house, use two RCD spurs and they can run as a TT system down by the pool.
Lucien seems to have written out the capacitance idea, grabbing at straws really, so two different potentials does seem the most logical way to look at it.
Did you check the continuity of ALL the cores and the wire armour before doing the IR?

Too many people do R1 + R2 , but few seem to do Rn + R2 ...... which can be very revealing
 

Lucien Nunes

-
Mentor
Arms
Esteemed
onto something with the different earth potentials
Seems unlikely. The RCD can't sense earth potentials, only the imbalance between line and neutral currents, two conductors that you claim are effectively insulated from earth.

If there is a difference, there is leakage, but it matters not where the leakage takes place or where it goes; The circuit's own CPC, another earth near neutral potential, a rogue 'earth' at some other potential, another circuit's neutral. It can be inward leakage from another circuit's line to the protected circuit's neutral, or even into its line from another line on a different phase. Any or all of these combine to give a particular figure for imbalance which is what the RCD detects. A few volts difference between one leakage 'destination' and another won't affect that total more than a gnat's.
 
As Lucien explains, the only way the RCD could trip is if there is a current path from L or N to earth, that's all the RCD can detect. The problem is investigating the fault when the RCD trips right away.

From your first post, all is well with the CPC connected with sheath isolated, but the RCD trips when the sheath is connected to earth, is that correct? It's weird that should happen while you can't find any leakage with the meter at (say) 500V sheath-L, but that must be where the current is going (also possibly sheath-N).

You could try connecting the sheath to the CPC through a 10k
Ω resistor, value isn't critical but it should be rated at 500V+ and be large enough to avoid tripping the RCD. That would let you check the circuit under fault conditions without losing the supply. You may get an indication of what's going on by measuring the voltage across the resistor. 230V would mean a low resistance sheath-L. A small voltage could indicate low resistance sheath-N which could be confirmed by disconnecting N from the supply, when the voltage would drop to zero.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
I have to say I am very much with Murdoch's line of reasoning at the moment. Have you with 100% certainty identified the conductors throughout, and proven that the core connected to the armour is indeed the CPC and not actually the neutral due to a discrepancy in labelling at the two ends?
 

Intoelectrics

-
Arms
Esteemed
@Arewehere,

please do post your findings, even if it turns out to be an error on your part. We all make mistakes so don't worry about any ridicule.:p

But it would be interesting to us if it turns out to be some gremlin in the system.

Look forward to your findings :)
 