Hi,

Customer wants me to fit him a 16A socket so that he can plug his caravan in, PME supply.

I wouldn't call his drive way a caravan site, so not exactly sure if I should be doing this as it could be potentially dangerous as I was just planning on hooking up the earth as well, but then thought would it need a rod?
 
I would not connect the PME system earth to the outdoor socket, I would put that one socket on it's own 30mA RCD and on it's own rod.

The RCD would be incorporated with that socket, and the rod local to it. (fed from a non-rcd way at the house)

It is not so much that the garden is not a caravan park, but more the difference between 'true earth' and the PME earth, bear in mind the caravan body and chassis is bonded to the earth locally at the van side.
 
Just thinking about this, it does clearly state in the regs that you don't take the earth to a caravan, which I knew.

I think I'll just tell him to stick with him after lead and plug it in to his 13a plug.

All I was going to do is change a faceplate for a commando socket basically for ease.

Whats the difference in having a proper socket or using an adaptor, the 13a plug version has the earth connected still, just I didn't do it.
 
If the customer hypothetically said to me I want a 16a socket but don't want to tell e it's for a caravan then I wouldn't have known.... Just seems stupid how you can plug it in a 13a and it's all of a sudden aacceptable.
 
As I said if you earth the van with the PME earth, you would have a bloody big piece of metal (the van) that may be at a different potential to the true earth (the garden), then the usual broken suppliers Neutral scenario also rears it's ugly head, the car charging points regs are the same/similar for the same reasons.
 
Just RCD/TT that socket.

It is for safety reasons, just think if the Van body became live because of a fault, and you were stepping in or out., one leg on the garden and one leg in the van, it basically covers your arse in the unlikely event blah..blah
 
As I said if you earth the van with the PME earth, you would have a bloody big piece of metal (the van) that may be at a different potential to the true earth (the garden), then the usual broken suppliers Neutral scenario also rears it's ugly head, the car charging points regs are the same/similar for the same reasons.


Except you can now use a PME supply for a car charging point!!

If this is just for a caravan battery charging point isolate the house earth and use a roded earth. I wouldn't be going overboard on the Ra values either, unless they intend to use that supply for anything other than charging the battery....
 
Except you can now use a PME supply for a car charging point!!

It is not quite as cut and dried as that E54, there are a number of caveats attached to your statement above.

It is too much of a generalising statement to say you can use PME for car chargers, yes you can but only if other circumstances/conditions are met, ie. it is conditional. or you have a very good reason for the exemption clause.
 

Attachments

Last edited:
So just to confirm then, if this was TN-S then I could just go ahead and connect it up with no issue as its not PME and could connect the earth and take it outside to the caravan and thats all ok.
 
It is not quite as cut and dried as that E54, there are a number of caveats attached to your statement above.

It is too much of a generalising statement to say you can use PME for car chargers, yes you can but only if other circumstances/conditions are met, ie. it is conditional. or you have a very good reason for the exemption clause.

Point taken, i was aware, but to rattle off all those conditions/provisions and it would have been a hell of a long post. lol!!.

It's a shame the DNO's don't insist on the provision of an earth rod for all PME/TNC-S installations, as they do in most other Western European countries....
 
As I understand it you can if you disconnect the PME earth.

The funny thing is, you could just get an adapter from a 16A to 13A plug top and plug it in on a PME anyway with no earth rod....

Do you feel that such adapters should be banned then.
 
UKsparks,

What you do is entirely up to you, we can only advise where you stand wrt regs, and why it is not a good idea to use the PME system earth for a caravan, whether it is in a park or the garden.

TT an TN-S supplies are no problem, it is only TNC-S/PME which gives problems on this type of install

Yes, you segregate the earths. here are the various drawings, although these are for full caravan pitches, the same principle applies to a single socket, Drawing 02 is the nearest one for your single socket, I have just included the others for information.
 

Attachments

  • caravan 01.jpg
    caravan 01.jpg
    56.4 KB · Views: 66
  • caravan 02 001.jpg
    caravan 02 001.jpg
    67.9 KB · Views: 64
  • caravan 03 001.jpg
    caravan 03 001.jpg
    74.5 KB · Views: 55
  • caravan 01.pdf
    caravan 01.pdf
    65 KB · Views: 50
  • caravan 02.pdf
    caravan 02.pdf
    76.5 KB · Views: 42
  • caravan 03.pdf
    caravan 03.pdf
    83.2 KB · Views: 43

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Market Harborough

Thread Information

Title
Caravan charging point / 16A Socket
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
uksparks,
Last reply from
uksparks,
Replies
25
Views
6,589

Advert

Back
Top