Discuss Cert filling? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
S
sixfingers
Hi,I have a question on cert filling on a domestic eic! The installation of 1 x new circuit on a exsiting installation would require an eic,But on the circuit details/test results page would you fill in details for all circuits or just the circuit you have installed and tested?
Just the circuit you installed and tested, making sure on the front page states exactley what you did ie new radial for hob.
As Jason said only the circuit you have installed, same goes for any installed circuits whether Domestiic, Industrial or commercial
100% agree but like the man said be as specific as you can on the front page where it asks for what is covered by this certificate.
If anything should go wrong with another part of the installation and you havn't been exact about what you did, the customers first words will be - well you were the last one to do anything...... and all of a sudden your in a whole world of pain.
Cheers guys for clearing that one up,Just a quick one so on complete fuseboard change you would put in the (details of installation) box, (fuseboard replacement only) but all old circuits connected to new board would be noted on the circuit details and test results page would we be liable for old circuits on only a fuseboard change?
Yes.
As you say details would be - upgrading of consumer unit only (having already confirmed earthing and bonding arrangements)
All circuits would be recorded on circuit details sheet and fully tested as per BS.
Should a problem arise at the end of any of those circuits then it would not be your fault as you have tested your work and only worked at the beginning of each and will have stressed in your extent covered box.
What he said ^^
Also, when you slap on all the warning notices on the new CU, i always mark the periodic label with date it was changed, and also put next to the date "CU CHANGE ONLY".
However, you should also list any deviations in the right box on the cert.
And there will always be a couple.
Cheers so a deviation from regs would be ie pendant fitted in bathroom or socket above kitchen draining board,so as long as they are noted in details of departures box or would they be noted in comments on existing installation box?
Kind of , yes.
However, any major ones should be rectified and charged accordingly.
I normally have a quick look round when pricing CU change and advise client.
no it would be a minor works cert as it is an addition
Sorry, Beaver, that's not right... the MInor Works Cert, states clearly that it can only be used for work that "does not include the provision of a new circuit."
Regarding comments on the EIC, etc., it's worth adding in the 'Agreed Limitations' something along the lines " cables and accessories inaccessible or concealed in the fabric of the building could not be inspected or tested."
Sorry, carried on reading posts and saw you've already dealt with this one!
incorrect all new circuits ,new being using a new circuit on the CDU ,the cert is an installation because youve installed a new circuit not added to an existing ,its also notifiable !
Reply to Cert filling? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
NICEIC Certification Scheme BS7671 Amd2 Cert completetion RCBO's
hey guys, Just completing an install cert for a new consumer unit and im a bit confused on PD selection. I install Type A RCBOS but on the new...
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Hi all I have been pulled up by Napit, not by my regular inspector. Used rcbo's on a rewire (usually do). Filled out cert to reflect this, with...
Not sure whether this is the right context or even forum to mention this, but I’ve recently been offering out myself to a friend to help get his...
Hi all, how do you go about filling out a EIC or a minor works certificate when you have multiple installers that have worked on the circuit...