Having recently installed a submain, sheath to TN-C-S earth at supply end, isolated and TT'd at the far end I'm a bit unsure on the cert.

I have ticked both earthing types but am stuck on how to separate the values for each installation to put them on the same cert. Max Ze for example, should this be Ze from the meter, or Ze of the rod 100 metres away? We've done nothing whatsoever with the installation on the far side, just the distribution and provided an earth.

Common sense is telling me to write our cert just for the distribution cable up to the external board, as someone else is doing all that side and certing it separately. If they had installed the rod it would have been simple as it effectively falls on their side of the installation, but obviously we need to note the rod's Ze somewhere.

Anyone done a similar installation before and overcome this confusion? If so HELP I'M GOING CRAZY!!

Thanks :)
 
Yes indeed TT is to an outbuilding, and I have included the details of the rod and Ra in the particulars of installation at the origin as it's the only place to put them. As that figure (whether we class it as Ze or Zdb) is already noted, I'll put the Ze using the TN-C-S earth down under supply characteristics. It says to put the higher value down if more than one supply, but doesn't mention if one supply and more than one earth. That seems to make the most sense, even though the rod is from a sub dist board and not at the origin. Cheers :)
 
hi mate have you used two schedule of test results one for the supply which will have your origin tn-c-s Ze and the other schedule for the ccu in your outbuilding with the tt Zdb which is also the Zs for the the circuit from your distribution board supplying your ccu in outbuilding
you have 1 eic ,1 schedule of inspections and 2 schedule of test results 1 for each board
 

Reply to Certificating distribution circuit which is TN-C-S one end and TT the other? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock