uHeat Banner - Forum Discount Available
Discuss Certifying new electrical installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
M
Modernelectric
I put in a shower circuit, new lighting circuit and swapped the consumer unit on a job.
To my understanding i must issue a new electrical installation certificate for the consumer unit swap, and a seperate certificate for the 2 circuits i installed. is this correct, or must the 2 circuits also have there own seperate electrical installation certs?
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
A
acat
  • #2
Hi the one installation certificate should cover all under "Description and Extent of the Installation" record what you have done and your inspection and test results will confirm what you have done.
Chris
M
Modernelectric
  • #3
ok thanks, so the consumer unit, shower circuit and lighting circuit i can cover with just 1 electrical installation certificate.
A
acat
  • #4
Thats the way I see it as your installation certificate covers everything from just adding one circuit to a complete install on a new dwelling.
Chris
sparkswillfly
  • #5
just eic as you have got to test every circuit the cu feed you have changed and take responsabillity for them
T
TPES
  • #6
Rather than start a new topic for a quick answer could someone help me out..
A fellow spark has an extension to wire, Extending the house ring main to the extension and extending the existing lighting circuit to the extension.
Its a 16th ed CU, the lighting on main switch, RFC on RCD.. The spark seems to think that aslong as the main/supplementry bonding is up to scratch then there's no need to alter the board at all, Does the lighting not need to be RCD protected to be upto date with the 17th regs ?? And its EIC right? Not MW?
Spudnik
  • #7
Yes the circuit worked on should be RCD protected UNLESS he is going to use steel conduit or dig out half the wall.
And MW is fine as its not a new circuit.
T
TPES
  • #8
I thought it would have to be RCD protected, But the spark thinks im wrong.. I thing he still working to 16th. Thinking aslong as the bonding is ok then that will do.
So if MW was issued would it be 2 certs for each circuit.
Also an EIC would be ok wouldnt it if the box "Alteration" was ticked then both circuits on one cert?
Spudnik
  • #9
One cert for each circuit, although you could do an EIC with only the circuit details that you worked on.
Personally i would just do 2 MW, one for each.
supertoad
  • #11
i tend to put in a seperate cu for the extension,[check Ze FIRST], then only need to certify the new work done! no overlap,some customers try to get there substandard existing system certified for the same price!! one set of forms should be new install cert ,the other would be a condition report[old PIR]-hope this helps
HandySparks
Mentor
I expect the OP has finished the job by now. :smile:
Welcome to the forum.
R
rattlehead85
  • #14
To clarify. If he changed the C.U but has only worked on the ring and lighting, when he completes his EIC does he only need to fill out results for these circuits or is he now responsible for all circuits to the dwelling as he has replaced the C.U serving them?
O
Octopus
  • #15
If he's changed the CU he would of course have tested all the circuits - old and new.
CK Tools :) The professionals choice when it comes to Electrical Tools
Reply to Certifying new electrical installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Top Bottom