On a recent EICR i have measured 0.589 MegOhms (@250 volts) on the relatively old lighting circuit (red/black PVC wiring) , i have replaced both outside lights (thinking water ingress as both were damaged).

The strange part is at 1000 volts the IR changes over a few seconds to 1.6 Megohms , it will stay at this value even at 250V for perhaps an hour.

Its a void property and been empty for a few months if this helps?
 
P

Petej999

Arms
Reaction score
80
On a recent EICR i have measured 0.589 MegOhms (@250 volts) on the relatively old lighting circuit (red/black PVC wiring) , i have replaced both outside lights (thinking water ingress as both were damaged).

The strange part is at 1000 volts the IR changes over a few seconds to 1.6 Megohms , it will stay at this value even at 250V for perhaps an hour.

Its a void property and been empty for a few months if this helps?
Damp getting in somewhere I think
 