Have a customer who wants to swap the broken shower for a direct replacement same make load etc is this ok to change if there is no rcd or should I tell them that this must be fitted.
 
Like for like swop using existing wiring = no need for rcd to be added IMO.
Its prefered , but not mandatory.
The installation will be no more unsafe than before will it ?
 
had a customer afew weeks back bought a 9.5kw shower that they wanted me to fit. Cable run ran within a plastered wall,then insulated (rock wool) stud work, across extra insulated loft (free insulation crew had been in), pull switch then back in loft to shower. Cable run was about 28metres so worked out 10mm t&e needed.......BUT manufacturers instructions stated for a run of 30metres 6.0mm was fine (no other info about diversity given).

Knowing it needed to be 10mm but instructions claiming 6.0mm is fine where does this manufacturer's stuff fit in with that????

After much conversation and having to prove calcs to customer (secondary school maths teacher of all things) eventualy agreed 10mm needed at extra expense.
 
Dont forget that the manufacture instructions are based on several different models.

a 6mm would be fine for any shower under 8.5kW.

I would still say have to be 10mm as a min for a 9.5kW shower - see your point though with the maths teacher
 
had a customer afew weeks back bought a 9.5kw shower that they wanted me to fit. Cable run ran within a plastered wall,then insulated (rock wool) stud work, across extra insulated loft (free insulation crew had been in), pull

Iswitch then back in loft to shower. Cable run was about 28metres so worked out 10mm t&e needed.......BUT manufacturers instructions stated for a run of 30metres 6.0mm was fine (no other info about diversity given).

Knowing it needed to be 10mm but instructions claiming 6.0mm is fine where does this manufacturer's stuff fit in with that????

After much conversation and having to prove calcs to customer (secondary school maths teacher of all things) eventualy agreed 10mm needed at extra expense.

In this situation i dont see how a manufacterer can specify 1 cable size is the same or adequate for all installations ? and at 28mtrs volt drop may be significant.
You did right , carry out your own assessment.
 

Reply to changing over shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
987
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
  • Sticky
A recent thread on the suitability of a cable supplied preinstalled on a manufactured floodlight/pump had me wondering a few things. Over the...
Replies
4
Views
826
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock