Hello,
I would like to install a 40 amp EVSE on the outside of our garage, immediately next to our main panel and meter. We have 200 amp service. The main panel has two 100 amp breakers. Each feeds a sub panel - one in the garage and the other farther into the house. The garage sub panel has a slot for a new breaker and could accommodate a new dedicated 50 amp circuit for the EV. Connecting to the garage sub panel will require a 25+' conduit run, however.
Is there a simple way to power the EVSE from the main/meter which is immediately adjacent? This would avoid the costly conduit run to the garage sub breaker. Note that the main panel doesn't have any open slots. The two slots are filled with breakers that feed the two sub panels.
Tx!
need megawatt on this as it's US, butmy first thoughts would be to supply from panel breaker (of the correct rating).
I would be considering changing the main panel next to the meter from a 2 way panel up to a 4 way panel.
Hello,
Tx!
If you are talking about tapping in the meter base no. If you are going to do this job spend a little more money and do it the correct way. If you feed is 25+ feet and it will be underground then you can use direct burial wire with no conduit. It will also require a disconnect at the charger
Reply to Charging EV via meter/main breaker in the UK Electrical Forum area at ElectriciansForums.net
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
I have an interesting scenario that could use some feedback. I have 200A service in my home with a sub panel running to a detached garage...