Hi could sombody please help, im currently coving cable calculations and volt drop. I understand the process and how to determine csa but could sombody please help me out as to where there is a table in bs 7671 ci to size of insulation. I found this table on line and just wondering if theres anything similar within the 17th edition, i cant find anything in appendix 4.
Table 4.5 - Derating factors (CI) for cables up to 10mm² in cross-sectional ---------------- area buried in thermal insulation. | |
Length in insulation (mm) | Derating factor (CI) |
50 | 0.89 |
100 | 0.81 |
200 | 0.68 |
400 | 0.55 |
500 or more | 0.50 |