Discuss Circuit design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all!
When you are designing new circuits, do you design for both overload and fault protection for every case? Or for fixed loads design without overload protection and make adiabatic check as well?
I usually find that when the adiabatic equation is used the earth conductor size is suprisingly small, and that the CPC size in T&E is always more than adequate.
But as far as designing a circuit goes I think you are always supposed to make the calculation unless CPC is the same size as the line conductors.
The design procedure is:
1) Calculate design current (applying diversity if nessessary)
2) Select MCB
3) Select cable based on MCB and check voltage drop.
4) Calculate Zs (Ze+R1+R2) and then fault current
5) Calculate minimum CPC size using adiabatic
Reply to Circuit design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
I'm doing an design project at college and are onto my cable calcs now and I'm fine with my lighting circuits and the fridge and dishwasher...