Hi All

I have been asked to install a New DB to serve 40 offices, with the facility to meter each office individually.
I was thinking of installing a 18way TP&N DB, running 10mm to each office where a smaller SP CU is installed branching off to 3 circuits. Lights, Sockets and electric heater. A Din Rail Energy Monitor would be installed in this CU.

Whole install is in Dado and plastic trunking on the surface so RCD is in the office CU and not the 3P&N DB.


Any thoughts on this or any other way of doing it.
 
What type of protection were you thinking of using for the sub-mains?
You can get SP boards with meter packs these days which also have communications options so these meters could all be remotely monitored
 
What type of protection were you thinking of using for the sub-mains?
You can get SP boards with meter packs these days which also have communications options so these meters could all be remotely monitored


Any links would be greatly appreciated.

I was thinking just MCB protection in DB and RCD in Sub SP Board.
Thinking no requirement for RCD between DB and SP Board as the supply is in trunking
 
Any links would be greatly appreciated.

I was thinking just MCB protection in DB and RCD in Sub SP Board.
Thinking no requirement for RCD between DB and SP Board as the supply is in trunking
Any non-domestic board should have various meter pack options these days

So you arent interested in providing any discrimination between ocpds then?
 
3KW approx per room.
Total of 30-40 offices on this DB.

Offices will have 5 double sockets (PC use), 1 x 1KW Heater and LED Lighting

Edit: link didn't work

might be better to use something like these for the distribution circuits.
 

Attachments

  • Circuit Metering LS201 - EletriciansForums.net
    LS201.jpg
    25 KB · Views: 76
Last edited:
http://www.hager.co.uk/product-catalogue/energy-distribution/protection-devices/fuse-carriers/hrc-fuse-carriers-bs88/ls201/47120.htm

might be better to use something like these for the distribution circuits.


Whats the benefit of using these?
I was thinking MCBs are readily available and anything else the client wants to add later on they can.
 
Any non-domestic board should have various meter pack options these days

So you arent interested in providing any discrimination between ocpds then?

What do you mean about discrimination of over current protective devices?
There will be a 50A MCB in the DB, and in the CU there will be 32A - Sockets, 16A - Heater and 6A Lighting.
They wont even get anywhere near this.

The offices are single occupancy offices so they should not even use 20A day to day.
 
Whats the benefit of using these?
I was thinking MCBs are readily available and anything else the client wants to add later on they can.

would provide better discrimination. you will struggle to achieve discrimination between MCB's. For example a fault on the lighting circuit in the office could just as easily trip the MCB feeding the distribution circuit taking out the computers.
 
What do you mean about discrimination of over current protective devices?
There will be a 50A MCB in the DB, and in the CU there will be 32A - Sockets, 16A - Heater and 6A Lighting.
They wont even get anywhere near this.

The offices are single occupancy offices so they should not even use 20A day to day.

With respect, are you sure you are qualified to design an electrical installation of you don't understand the principal of discrimination of ocpds?

Look at the manufacturers data including tripping curves and times for the MCBs to see how they will discriminate
 
Last edited:

Reply to Circuit Metering in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock