could someone give me some help calculating a circuit resistance for a single phase circuit as it would be entered on a minor works cert if tested?

the circuit in question is a supply from a 2.5mm T&E 30m long going to fused spur then into 1.5 T&E 15m Long.

1st is the calculation done as two seperate calcs one for each cable size or just for the smaller cable?

also if i have a Ze of 0.8 how would i do the working out for the correct r1 + r2 for this circuit?

i think i have one over too much information and confused myself!!!!!
 
could someone give me some help calculating a circuit resistance for a single phase circuit as it would be entered on a minor works cert if tested?

the circuit in question is a supply from a 2.5mm T&E 30m long going to fused spur then into 1.5 T&E 15m Long.

1st is the calculation done as two seperate calcs one for each cable size or just for the smaller cable?

also if i have a Ze of 0.8 how would i do the working out for the correct r1 + r2 for this circuit?

i think i have one over too much information and confused myself!!!!!

Are you talking about insulation resistance or r1 + r2? r1 + r2 should be taken from direct measurement or do a zs test and subtract ze to get r1 + r2
 
Is it a tns? can you take a direct measurement of r1 + r2?

zs = ze + r1 +r2


the measurement on my megger for r1 + r2 is coming up as 0.22 and the Zs reading is 0.6 can this be right or am i missing something here?

the measurement on my megger for r1 + r2 is coming up as 0.22 and the Zs reading is 0.6 can this be right or am i missing something here?
 
Last edited by a moderator:
the measurement on my megger for r1 + r2 is coming up as 0.22 and the Zs reading is 0.6 can this be right or am i missing something here?

Sounds like parallel paths try disconnecting your bonding and doing zs again
Your ze is definately 0.8? is it a tns system?
 
Last edited by a moderator:
is this measurement wrong then? what should the R1 + R2 compared to Zs 0.6 or vice versa Be!! im def confused now if i disconnect bonding and put that on a minor works certificate wont this not be incorrect readings for circuit being tested once bonding reconnected and put into service
 
is this measurement wrong then? what should the R1 + R2 compared to Zs 0.6 or vice versa Be!! im def confused now if i disconnect bonding and put that on a minor works certificate wont this not be incorrect readings for circuit being tested once bonding reconnected and put into service

Like i said before it should be zs = ze + r1 + r2, sorry bud if you don't know how to work these out you should'nt be doing the work anyway
 
Are you talking about insulation resistance or r1 + r2? r1 + r2 should be taken from direct measurement or do a zs test and subtract ze to get r1 + r2

Whilst Zs can be measured or calculated I don't believe you are allowed to subtract your Ze from Zs to give you (R1+R2). Don't forget parallel paths would be included.

Someone also mentioned disconnecting bonding. This should never be done on a live installation - as such you cannot measure Zs with an EFLI tester with the bonding disconnected.
 
Last edited:
zs=ze+(R1+R2) you can use this to calculate for zs but not for (R1+R2)

Sorry guys my mistake, i personally always measure everything anyway so never do the calculations to work the stuff out i just know the relationship between them all, its been a long week and my head is fried:D
 

Reply to circuit resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
790
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
267
For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on...
Replies
6
Views
810
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock