Discuss Circuit tripping with tranformers. in the Australia area at ElectriciansForums.net

T

toast

I have just replaced some dimmable transformers.
But they keep tripping the circuit, the transformers a new and I installed first without a dimmer switch.
If I disconnect them the circuit stays closed, is there a way to test the transformers?
 
More info would be helpful. Are the transformers electronic or wire-wound? Are they supplying low voltage downlights (ELV halogen dichroic lamps)? How many lamps on the dimmer and what wattage are the lamps? Is the circuit configured with one transformer per lamp? What is the dimmer rated at? What size circuit breaker is the circuit tripping? Does it trip immediately or after the circuit has been running for a while?
 
Thank you for the question and sorry for late reply.

I will give as much info as possible:
The transformers serve single M16 50watt lamps, there are only two in this location.
Transformers are rated at 230/240v, 20-60W.
http://www.bizflips.com/library/pdf/DOT

The transformers were not connected to dimmer at the time as the dimmer was also faulty, but now replaced for 400watt rated so plenty enough for load.
The lighting circuit is protected by B type 6 Amp device, as soon as the circuit is closed the MCB trips, this is without the lamp being in place, just the transformer. If I remove the transformer from the circuit the circuit does not break. If I install standard pendant light without transformer connected everything works fine.
No problems with continuity or IR and Zs is in compliance for 6A B type.
The lighting circuit is not protected on the RCD side, only MCB trips.
It can only be faulty transformer, can they be tested?
 
Last edited by a moderator:
ELV transformers operate at about 50KHz and are difficult to test unless you have a suitable tester that can test at this frequency, the most testing I do is to see if they work (which they do not seem to in this case). Normally I feel that the time taken to remove, test and reinstall is greater than the time taken to just replace a £4 component.
However you could do a continuity check between line and neutral since the MCB is tripping instantly it is a very high current and likely to be on the input side. If you get less than 7ohms then there is an internal short, take the new transformers back and get working replacements.
 
Thank you for the question and sorry for late reply.

I will give as much info as possible:
The transformers serve single M16 50watt lamps, there are only two in this location.
Transformers are rated at 230/240v, 20-60W.
http://www.bizflips.com/library/pdf/DOT

The transformers were not connected to dimmer at the time as the dimmer was also faulty, but now replaced for 400watt rated so plenty enough for load.
The lighting circuit is protected by B type 6 Amp device, as soon as the circuit is closed the MCB trips, this is without the lamp being in place, just the transformer. If I remove the transformer from the circuit the circuit does not break. If I install standard pendant light without transformer connected everything works fine.
No problems with continuity or IR and Zs is in compliance for 6A B type.
The lighting circuit is not protected on the RCD side, only MCB trips.
It can only be faulty transformer, can they be tested?

I'd replace the tranny - then return it to the supplier.
 
Thanks again for the replies,
I have removed the transformers, with the intention to return for refund next time I am at the wholesalers.
I spoke to the customer and decided to do away with them all together and replace with GU10s.
Everything works fine now.
It's the first time in two and half years the customer has had all his lights operating correctly.
 
Thanks again for the replies,
I have removed the transformers, with the intention to return for refund next time I am at the wholesalers.
I spoke to the customer and decided to do away with them all together and replace with GU10s.
Everything works fine now.

It's the first time in two and half years the customer has had all his lights operating correctly.

and there speaks common sense.
 

Reply to Circuit tripping with tranformers. in the Australia area at ElectriciansForums.net

Similar Threads

Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Replies
2
Views
983
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
383
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
277

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock