How do you size the MCB, wire and protection for a motor in the UK/Europe? How is it typically done?
If anyone is curious here how its done in the US:
You size the conductor based on 125% of tables 430.247-430.250 determined by the type of motor and duty cycle of course. (When Table 430.249 says 2 phase they don't mean 180* out of phase like in 120/240 but 90* out of phase- this was common 100 years ago during the electrification of the United States but obsolete today)
This will then take you to table 310.15 B 16:
60*C or 75*C based on your wire and termination. Typically you use 75*C, and de-rate (more than 3 conductors in a conduit) off the 90*C column as THHN/THWN is rated 90*C. Once the conductor size is known you size the fuse/breaker based on Table 430.52.
For a breaker you can size at 250% of the conductor's ampacity (current carrying capacity), for a none time delay fuse 300% and for a time delay fuse 175%.
Remember there is no loop impedance requirement- meaning you can place #14 (2.08mm2) on a 40 amp breaker and run it as long as you like, ie 500 feet or more.
Next, you size the motor's overload protection based off 115% to 125% of the motor's actual nameplate rating.
If any of you have 3 hours time to burn, here is a crash course on the subject;
Over all idea under the NEC:
View: https://www.youtube.com/watch?v=_7FmwY442dQ
Sizing the breaker/fuse (Short circuit and ground fault protection of the wires):
View: https://www.youtube.com/watch?v=nvJaaWGJMo0
Sizing the conductors:
View: https://www.youtube.com/watch?v=Sic1uoua3og
Sizing of the overload protection for the motor and wires:
View: https://www.youtube.com/watch?v=2cprO8ZdT1U
Ambient Temperature
Table 310.15(B)(16) of the National Electrical Code lists the allowable ampacities of insulated general use conductors. This makes it a very useful table, but, we must keep in mind that the conductor...