• Please checkout this (ad-free) update post I've done on a spare blog. Feel free to bookmark it and check everynow and again for update if ads are pissing you off. Always feel free to ad-block them for now though if you want. I'll let you know when you can disable the ad blocker again, only if you want to see the ads. They should look nice and neat in the end.

Discuss Clarification on additional sockets on a spur in the Electrical Forum area at ElectriciansForums.net

Reaction score
16
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Evening all

Got a query excuse me if not seeing the simple logic. On reading regs book it states can install one unfused spur off ring in 2.5 but if more sockets required need to first wire through a fused spur. My question is, is this all because of possibility of overloading one leg of the ring or is it to protect the first cable coming off the ring? If this is the case can any justification be made if ran a 4mm off the ring to first socket and then a 4mm to second. Thanks
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
67,260
the reg.for fusing down is mainly to protect the spur cable (generally 2.5mm) from overload as the ring is protected @ 32A. if you were to install an unfused 4mm spur with several sockets, you run the risk of putting too muck load on 1 point of the ring, esp if it were close to one end of the ring.
 
OP
J
Reaction score
16
the reg.for fusing down is mainly to protect the spur cable (generally 2.5mm) from overload as the ring is protected @ 32A. if you were to install an unfused 4mm spur with several sockets, you run the risk of putting too muck load on 1 point of the resp if it were close to one end of the ring.
Thanks Tel. So if a 4mm is used as initial cable of the ring this is then protected against overheating. If as you said though that socket coming off is at one end of ring is there now a over heating danger to one of these or is it just that because current isn't spread around ring adequately that it is just likely to trip out?
 
R

radiohead

In practice it does not matter at what point on a ring a spur comes from.
In the case of an unfused spur feeding a twin socket then potentially a load of 26a could be drawn at that point on the ring. With a fused spur the number of sockets on the load side is unlimited because overload protection @13a protects the spur cable both upstream and downstream from the FCU.
So in theory a fused spur is far less likely to result in excess load on one point of the circuit. But unfused spurs are far more common than fused spurs. In practice diversity and spread of load means 2.5mm ring circuits are rarely stressed unless poorly designed for known high load situations like commercial kitchens.
 
OP
J
Reaction score
16
What do you want to get around? If you ran 4mm, depending on correction factors you could most likely run it as a radial anyway with the 32A MCB.
In practice it does not matter at what point on a ring a spur comes from.
In the case of an unfused spur feeding a twin socket then potentially a load of 26a could be drawn at that point on the ring. With a fused spur the number of sockets on the load side is unlimited because overload protection @13a protects the spur cable both upstream and downstream from the FCU.
So in theory a fused spur is far less likely to result in excess load on one point of the circuit. But unfused spurs are far more common than fused spurs. In practice diversity and spread of load means 2.5mm ring circuits are rarely stressed unless poorly designed for known high load situations like commercial kitchens.
Thanks radiohead is there any scenarios then you would be comfortable doing what I proposed....2 double sockets off 4mm from ring.
[automerge]1595185833[/automerge]
If you require more than one additional socket then just split & continue the ring circuit
It's option dazzler but this job I'm already having to cut hole in plasterboard and another hole in skirting just to get a cable through trying to keep holes and trunking down to minimum
[automerge]1595185881[/automerge]
What do you want to get around? If you ran 4mm, depending on correction factors you could most likely run it as a radial anyway with the 32A MCB.
No chance of running new circuit TJ have to come off existing ring
 

7029 dave

-
Mentor
Esteemed
Arms
Reaction score
3,849
IMO, you dont have any choice other than extending the RFC, or spur off with 13amp switched spur then you can run as many as you like. (radial off the spur)

Personally I Dont like the latter
 

Reply to Clarification on additional sockets on a spur in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
747
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
1K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
396
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
504
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
4K
Advertise Here

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top