The answer is belt and braces. You can use one continuous piece of cable to bond the gas and water. Also it is bonded via the actual boiler when it is working. HOWEVER. if the boiler is changed when it is of the wall you lose the bonding provided by the boiler which is dangerous. When I have taught gas engineers I have instructed them all to use a temporary bond ie it looks a bit like a set of jump leads when you fit a new pump as again the bond is lost when you take the pump out. It has resulted in a plumber being killed when he touched both ends of the pipe at the same time.Hi. Could someone please clarify bonding requirements for me please. I know requirements are to have a seperate 10mm earth bond conductor for water and gas or that these can be in one cable if looped between each other. I have been working in a couple of properties lately that are in residential blocks. The both have combi boilers installed. I have noticed that they don't have any seperate bonding to gas. Just one 10mm that goes to water. Is this in breach of current regs? Thing i dont quite understand is as far as I am aware all pipe work of combi boiler is interconnected so if the bond the water pipes is in place then in effect the water and gas pipes of boiler are also aren't they? If this isn't adequate and a dedicated gas bond needs to be provide is the any solution to situations where meter is situated outside apartments and can't find where enters property or where access in a near on impossibility. Any advice/clarification be appreciated
also it does not take much time or materials to be sure. live long and prosper.