Hi All
DO NOT RELY ON THE SWA WIRE SHEATHING FOR EARTHING TO AN OUTBUILDING !!!!
Disconnect one end of the sheathing and use it only as an earth protection for the feed cable. Then provide a dedicated earthing method for the out building.
It is unlikely the steel sheathing will give you an acceptable test result.
See the Dave Ward videos on TT

Obviously you can't use the sheath, it's made of plastic!

There's no reason you can't use the steel armour of the cable though, that's one of the things it is designed to do!

The steel armour will give you perfectly acceptable test results if it is installed correctly.
 
Hi All
DO NOT RELY ON THE SWA WIRE SHEATHING FOR EARTHING TO AN OUTBUILDING !!!!
Disconnect one end of the sheathing and use it only as an earth protection for the feed cable. Then provide a dedicated earthing method for the out building.
It is unlikely the steel sheathing will give you an acceptable test result.
See the Dave Ward videos on TT
What would you consider to be an acceptable test result?
Watching videos is not a bad way to learn some information but the particular site and circuit layouts can massively affect the type of protection required.
therefore a full understanding of the differences in earthing types is likely to be required before you can say what is or is not acceptable.

I would say that as the installation is TT earthing throughout then there is no advantage in separating the earth of an outbuilding to the earth of the supply
 
Hi All
DO NOT RELY ON THE SWA WIRE SHEATHING FOR EARTHING TO AN OUTBUILDING !!!!
Disconnect one end of the sheathing and use it only as an earth protection for the feed cable. Then provide a dedicated earthing method for the out building.
It is unlikely the steel sheathing will give you an acceptable test result.
See the Dave Ward videos on TT
No no no no no no no
 

Reply to Class II enclosure + gland recommendation for divorcing SWA armour at TT outbuilding/shed? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
I would appreciate peoples thoughts on fixing this earthing setup to correctly separate PME & TT: Setup: Workshop at the bottom of a long garden...
Replies
31
Views
10K
So I've just been reading through the electricians guide to the building regulations for my own knowledge and have come across 2 regulations which...
Replies
20
Views
3K
I know the subject of transporting pme from a house to an out building has been discussed many times. This question is the DNO is only providing...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock