Just finished an EICR on an ex assisted housing flat, in a block of 4, since converted into normal flats.
Generally the condition isn't horrendous, a couple of damaged accessories(C1) but two odd ones.
1, The CU is in the meter cupboard, outside. Now it wasn't in too nad shape to be honest but there were some areas of light corrosion so I gave this a C3 and retest interval of two years. My reasoning being, it aint going to get better without attention and as things age the rate of damage will accelerate.
2, A shower circuit leaves the CU in 6mm brown and blue T&E and arrives in the shower in 10mm black and red T&E?
Ah the switch I hear you cry......
well the switch has 6mm black and red feed and load....answers on a postcard please.....
There are faults on this circuit quelle suprise.
Generally the condition isn't horrendous, a couple of damaged accessories(C1) but two odd ones.
1, The CU is in the meter cupboard, outside. Now it wasn't in too nad shape to be honest but there were some areas of light corrosion so I gave this a C3 and retest interval of two years. My reasoning being, it aint going to get better without attention and as things age the rate of damage will accelerate.