Just finished an EICR on an ex assisted housing flat, in a block of 4, since converted into normal flats.

Generally the condition isn't horrendous, a couple of damaged accessories(C1) but two odd ones.

1, The CU is in the meter cupboard, outside. Now it wasn't in too nad shape to be honest but there were some areas of light corrosion so I gave this a C3 and retest interval of two years. My reasoning being, it aint going to get better without attention and as things age the rate of damage will accelerate.

2, A shower circuit leaves the CU in 6mm brown and blue T&E and arrives in the shower in 10mm black and red T&E?

Ah the switch I hear you cry......

well the switch has 6mm black and red feed and load....answers on a postcard please.....

There are faults on this circuit quelle suprise.
 
There will be a joint between switch and shower where a section has been added to either move shower position or replace a section of heat damaged cable. Head in the loft space above bathroom would have revealed the joint. I'm gonna guess 30A choc block with a bit of tape round.

Is the current shower correctly co-ordinated with the ocpd and 6mm cable with the installed reference method ? I would also guess a larger shower could have been added from original at some point.
 
There will be a joint between switch and shower where a section has been added to either move shower position or replace a section of heat damaged cable. Head in the loft space above bathroom would have revealed the joint. I'm gonna guess 30A choc block with a bit of tape round.

Is the current shower correctly co-ordinated with the ocpd and 6mm cable with the installed reference method ? I would also guess a larger shower could have been added from original at some point.

OCPD, cable and shower all tally, there will be JBs a aplenty no doubt without the boxes.

FI on cert.
 

Reply to Code advice. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock