Hi folks. Would like advice/ discussion

What code should be given for the following
ImageUploadedByTapatalk1399633535.318192.jpgImageUploadedByTapatalk1399633549.500669.jpg

Now I am sure it's the same up and down the country data and power cables lashed together above ceilings ect.

There are various sections of dado, which PVC singles share the same compartment of the data. This quite rightly has been given a c2.
( there is no voltage rating on the data cables and am struggling to get info )

What I am concerned with is where twin and earth occupies the same compartment and shares the same cable routes above ceilings ect without physical separation.
With regards to reg 528

What I am getting at is is the sheath of the twin and earth an equivalent mechanical protection as in a barrier( if u get my meaning). As behind desks ect data and flexible cables are always entwined

Now obviously in an ideal world it would all be installed universe ceilings on basket tray ect and physicals expectation maintained throughout and metal/ steel conduit used for power. But nowadays every thing is twin and earth lashed up above no clips ect ect

Rant over

Thanks in advance
 
Last edited:
It is all C3. OK its a mess and it isn't compliant. you obviously realise that these cables should be in separate compartments, and they are not, but they don't pose any danger. The worst thing that could happen is someone gets a fuzzy picture on their screen, or they may get false alarm activations etc, but no one is going to get hurt either now or in the future from it.

C2 is only for non compliances that could pose a danger if is left unattended, a good example would be a crack in a socket faceplate, it isn't dangerous now, but if it gets worse it will be, and if it then exposes live parts it would become C1, and what you are faced with will never become a C1. But before anyone beats me up, please remember i am only basing my opinions on what i can see from 2 photos, i don't have the benefit of seeing anything else that the OP can see that may change my mind.

Cheers.............Howard
 
And I double concur with Mr Tel
 
Many thanks for taking the time to reply. You are 4 respected members, and I value your input.
I was having this discussion with another electrician. With looking at the regs ,on site guide and gn5 he was of the opinion it was a c2. As if I remember correctly in gn5 it says bands must both have the same voltage insulation rating to stop dangerous voltages appearing in band 1 circuits. I was on the fence as it would need 2 simultaneously insulation break downs for that to happen.

I agree with what Sirkit breaker said some codes are more clear cut than others. It is always good to bat things of like minded people like yourselfs

Thanks
 
If you think about it logically Jamie coding becomes fairly easy really, ok there's always going to be grey areas but-
1 Bloody dangerous right now! Do something about it or someone will get hurt
2 This is going to be dangerous if there's a fault, you should do something about this pretty quickly
3 Well it's not really dangerous but......
 
Many thanks for taking the time to reply. You are 4 respected members, and I value your input.
I was having this discussion with another electrician. With looking at the regs ,on site guide and gn5 he was of the opinion it was a c2. As if I remember correctly in gn5 it says bands must both have the same voltage insulation rating to stop dangerous voltages appearing in band 1 circuits. I was on the fence as it would need 2 simultaneously insulation break downs for that to happen.

I agree with what Sirkit breaker said some codes are more clear cut than others. It is always good to bat things of like minded people like yourselfs

Thanks

As with most things periodic, there is seldom a total agreement, and there will always be debate. Ultimately the person on the job has to make an informed assessment of what is in front of you and what might happen. So it is your call, we can offer our opinions, but for reasons in my original post i can only call it as i see it, but it isn't me filling the paperwork in. As long as you can make a good justification for any code you see fit to use, then you can only do your best.

Cheers.............Howard
 
If you think about it logically Jamie coding becomes fairly easy really, ok there's always going to be grey areas but-
1 Bloody dangerous right now! Do something about it or someone will get hurt
2 This is going to be dangerous if there's a fault, you should do something about this pretty quickly
3 Well it's not really dangerous but......

Trev I live my life in the grey :)
 
As with most things periodic, there is seldom a total agreement, and there will always be debate. Ultimately the person on the job has to make an informed assessment of what is in front of you and what might happen. So it is your call, we can offer our opinions, but for reasons in my original post i can only call it as i see it, but it isn't me filling the paperwork in. As long as you can make a good justification for any code you see fit to use, then you can only do your best.

Cheers.............Howard

Agreed. I know an electrician who works with royal sun alliance. His sole job is testing. I asked him about how they code things and was told five of us senior testers sat down hammered out/ agreed codes, and that's how we generally do it.

Why the hell people don't take time to do jobs properly/ use good workman ship I will never know. I would have got a size 10 up my butt.
 
it would need 2 simultaneously insulation break downs for that to happen.

Does it? In the case of singles then a single fault will expose the ELV cables to a voltage that their insulation is not rated for, so how would that take two faults? After all, the whole point is that we cannot confirm that they are sufficiently insulated against 230V. So in the case of the singles I can see a case for a C2, but ultimately - as said - it is a matter of opinion.
 
Does it? In the case of singles then a single fault will expose the ELV cables to a voltage that their insulation is not rated for, so how would that take two faults? After all, the whole point is that we cannot confirm that they are sufficiently insulated against 230V. So in the case of the singles I can see a case for a C2, but ultimately - as said - it is a matter of opinion.

Good point
There are sections where it has been done in dado in singles and points where it is done in flat sheathed twin
 
Does it? In the case of singles then a single fault will expose the ELV cables to a voltage that their insulation is not rated for, so how would that take two faults? After all, the whole point is that we cannot confirm that they are sufficiently insulated against 230V. So in the case of the singles I can see a case for a C2, but ultimately - as said - it is a matter of opinion.

What I was primarily getting at was in the case of the flat sheathed cables sharing the same containment
 

Reply to Code advice. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am only asking for YOUR opinion as to what code should be given in an EICR which sees a dry wall fixing box being used for joints behind a...
Replies
4
Views
1K
Hi there, We're currently having a new kitchen fitted and in the process we've had some new electrical work done. The electricains are comeing...
Replies
9
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Cabling above suspended ceiling the 600x600mm type tiling ceilings. Basically cables routed above ceiling’s no fixings, laid on top of framework...
Replies
13
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock