code 2 - requires improvement
code 4 - does not comply with BS7671

although the latter might not be strictly true it could be said it doesnt comply with 17th edition
 
You can not code a cu for having bs 3036 rewireable fuses if all tests prove satisfactory.
 
right old wylex type board change well ,bs 7671 requires all circuits up 32 amps to disconnect in .4 of a second not easy with rewireabled to achive that infact only real way to do that is an RCD , the other thing is that if the board is the type that has the wooden frame at the back the its classed as a code 1 , reason is if a fault developes in the board and they do an awful lot burnt terminals etc etc , then the wood becomes a fire hazard ,so a code 1 :D
 
right old wylex type board change well ,bs 7671 requires all circuits up 32 amps to disconnect in .4

Why can you not achieve this with a BS 3036 fuse without RCD?
 
they are in the regs and i accept they can be used but when you take into account the tripping current required to blow these fuses in the case of a low resistance fault not achieving the required current , the rcd will trip (well should do )having said that 60898 take a lot to trip ,ok ive dug a hole stick my head down it my error chaps
 
they are in the regs and i accept they can be used but when you take into account the tripping current required to blow these fuses in the case of a low resistance fault not achieving the required current , the rcd will trip (well should do )having said that 60898 take a lot to trip

I think you mean a high resistance fault wouldn't achieve the required current. If the Zs is below 80% of the max stated in BS7671:2008, then the fuse will blow within the required time, which is exactly what the tables are in there for!

RCD's won't trip on a line to neutral fault, and they also aren't infallible. I've found many on a periodic that refuse to trip at all, let alone in 0.04 of a second!

ok ive dug a hole stick my head down it my error chaps

That's what these forums are for, to all learn off each other! :)
 
Last edited:
Totaly agree think were all being led into a false sense of security there is a certain expensive make of RCB0/s ive never managed to test at the correct tripping times in fact the cheaper ones seam better

yep made an error :mad:

infact when you look at the real picture as electricians were told about RCD this that and the other ,all electric lawn mowers, trimmers,strimmer etc are class 2 and have no earth in the cables so an rcd to protect you when you cut the cable in half is useless !!
 
Last edited by a moderator:
right old wylex type board change well ,bs 7671 requires all circuits up 32 amps to disconnect in .4 of a second not easy with rewireabled to achive that infact only real way to do that is an RCD , the other thing is that if the board is the type that has the wooden frame at the back the its classed as a code 1 , reason is if a fault developes in the board and they do an awful lot burnt terminals etc etc , then the wood becomes a fire hazard ,so a code 1 :D


Unfortunately there are sparks who see a rewirable board as a throwback to some distant unsafe era,then recomend.usually totally unjustified advise that they are somehow non compliant and/or dangerous

There is a big misunderstanding amongst our industry with regard to this, and sometimes un necessary cost to the customer based on this ill thought out advise

Rewirable boards often come with a bakelite rear plate for fire issues
Even where they are not fitted,more often than not they are mounted on stone or brick
Overheating or faults occuring have little or no more chance of burning than a plastic enclosure of the modern board
Obtaining readings that would render the circuit unsafe are few and far between
The most obvious case is where 1.0mm cpc on a ring with a 30 amp fuse and a long length of cable has been used
Test and calculation usually allows dis connection times to be met

To all who have this unjustified mis understood aversion to 3036 fuses I say
Get to know your enemy first,he might be much less of a threat than you were led to believe

Another point is that this mis understanding is also used by rip off merchants to gain un necessary work
Our job is to make and test installations for safety,not to advise wrongly on installs that are acceptable and mostly compliant
 

Reply to Code for board chage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
How would you code a bathroom with all insulated fittings , no supplementary bonding and not supplied by rcd . The old BPG4 seemed to suggest its...
Replies
4
Views
988
With regards to Regulation 531.3. 3 of BS 7671:2018+A2:2022 Older AC type RCD's are prone to being blinded by dc leakage from other items plugged...
Replies
47
Views
6K
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
919

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock