Innominata
Hi Alll,
Anybody suggest code for board change from old rewirable.
Thanks
Anybody suggest code for board change from old rewirable.
Thanks
Discuss Code for board chage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi Alll,
Anybody suggest code for board change from old rewirable.
Thanks
right old wylex type board change well ,bs 7671 requires all circuits up 32 amps to disconnect in .4
Why can you not achieve this with a BS 3036 fuse without RCD?
they are in the regs and i accept they can be used but when you take into account the tripping current required to blow these fuses in the case of a low resistance fault not achieving the required current , the rcd will trip (well should do )having said that 60898 take a lot to trip
ok ive dug a hole stick my head down it my error chaps
right old wylex type board change well ,bs 7671 requires all circuits up 32 amps to disconnect in .4 of a second not easy with rewireabled to achive that infact only real way to do that is an RCD , the other thing is that if the board is the type that has the wooden frame at the back the its classed as a code 1 , reason is if a fault developes in the board and they do an awful lot burnt terminals etc etc , then the wood becomes a fire hazard ,so a code 1