Discuss codes in the Australia area at ElectriciansForums.net
Hey Lionel.
Code 1 = Requires urgent attention
Code 2 = Requires improvement
Code 3 = Requires further investigation
Code 4 = Does not comply with BS 7671
These codes are applied to any issues found on a periodic inspection and range from very bad i.e Code 1 - access live parts, absence of earthing conductor to Code 4 - no indicator sleeving on switch wires, no circuit schedule at DB.
Hope this helps.
Do the codes only apply when carrying out a periodic inspection report??,
and also what do you need to do if you come across a code 1, do you stop everything and make safe etc?..:)
Hi Dan.
Well the only time you would need to assign a code to an item is when you found it on a PIR and noted it in on the relevant page. If you found a problem whilst carrying out some other work then you could class it as one of the codes and note it in the comments on existing installation box on the EIC/MW you were doing for the work you had carried out.
Ideally yes a code 1 should be rectified straight away without delay.
Hope this helps.
An extract from professional electrician Nov 2008
Code 1 REQUIRES URGENT ATTENTION
Indicates immediate danger
The installation is a risk to the user; therefore , the inspector should take appropriate action without delay to remove the danger
Code 2 REQUIRES IMPROVEMENT
This code should be used to indicate that the observed fault requires action to remove Potential danger
CODE 3 REQUIRES FURTHER INVESTIGATION
Indicates that the inspection has revealed an apparent deficiency which could not be fully identified and
should be investigated further
CODE 4 DOES NOT COMPLY
With the current edition of BS7671 but are not deemed a risk to the user
hth Jim
Reply to codes in the Australia area at ElectriciansForums.net
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...