Simple quick question

Im going to put a new feed to a boiler, into a switched spur as it is now..

The cable being used at the moment is black rubber flex with a 3a fuse. (not sure if this was done right in past)

What size cable do i replace this with..?

Is 0.75 heat resistance flex Ok on a 3a fuse? or does it have to be bigger csa?
 
Normally a 5A switch fuse supplying a (modern) combi boiler. Heat res flex only really needed for Immersion Heater supply...most modern boilers are "cool touch", negating the need for a heat resistant cable.
hope this helps
Randyrat
 
Oops....forgot to answer the question.....
Depending on factors such as ambient temp etc which derate the supply cable, as a rough guide a 1mm cable will cope with 15.5 amps clipped direct...plenty!! Obviously if its a hundred yards long through insulation you need to perform the full calcs to determine current carrying capacity. If in doubt go large!!!!
 
Simple quick question

Im going to put a new feed to a boiler, into a switched spur as it is now..

The cable being used at the moment is black rubber flex with a 3a fuse. (not sure if this was done right in past)

What size cable do i replace this with..?

Is 0.75 heat resistance flex Ok on a 3a fuse? or does it have to be bigger csa?


hi there

small world a city and guilds design project has this in it !
i have run to the spur in 2.5mmm2 but from the spur to the combi is left to the designer

answer look at the manufactureres installation instructions


cheers
 
hey guys

what cable size/type would u use in a plug point for a boiler? I have a friend installing a boiler and shes asking for a plug point up in her loft? Wanted to know if i could help.

thanks..

nick
 
See the comments above. Size the cable(flex) in relation to demand info. Preferable to have heating supply on it's own radial to a SFS, appropriately fused, not off a RMF.
Regards.
 

Reply to Combi boiler feed..? in the Australia area at ElectriciansForums.net

Similar Threads

The new Advance Combi Boiler has a feed from consumer unit using 6mm cable on a 32amp breaker to a 45amp double pole switch. What size cable to...
Replies
9
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
Replies
43
Views
5K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm sure this question has been asked to death, so apologies! But just wanted some direct confirmation that my intended wiring setup is going to...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock