I have been asked to perform a pir on a property i know (belongs to my girlfriend) as we have tennents moveing in. My main concern is that a combi boiler is fitted in zone one. This was fitted about 4 years ago by a local plumbing firm.


How do you suggest i go about the rectification of this with the plumbing firm. They have just issued a landlords safey certificate.

It was intresting that they noted a undersized bonding conductor on the incomming gas but nothing about the boiler location.
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
S

Spudnik

  • Thread Starter Thread Starter
  • #2
Can you build a cupboard round it?
 
W

Wotsit

  • Thread Starter Thread Starter
  • #3
No, the manufactures instlation instructions reccomend a clearance that would put the cupboard over the bath just where your chest would be if you were lying there.

At the monent you can look up and see the underside of the boier if you are in the bath
 
Last edited by a moderator:
S

spark1

  • Thread Starter Thread Starter
  • #4
Wotsit, areyou saying that the combi boiler is in zone 1; within a shower enclosure or is directly over a Bath ??????



spark1
 
W

Wotsit

  • Thread Starter Thread Starter
  • #5
Wotsit, areyou saying that the combi boiler is in zone 1; within a shower enclosure or is directly over a Bath ??????



spark1
Yes just that, right over the bath.
 
S

spark1

  • Thread Starter Thread Starter
  • #7
Yes , sorry, I never worded that very well I was trying to confirm that wotsit had his zones correctly identified,,,,from his last post he has verified that.

My answer to the o.p. is to issue the P.I.R. with a code 1 on the boiler. It must be classed as Electrical equipment as it contains electrical parts therefore it requires IP X4 minimum....I take it the supply circuit is Rcd protected otherwise a Code 1 or 2 would be applicable also...either way " unsatisfactory on the Report...and send the Plumbers a copy asking for their comments.


spark1
 
Last edited by a moderator:

Des 56

-
Arms
Esteemed
It was intresting that they noted a undersized bonding conductor on the incomming gas but nothing about the boiler location.
That is probably because their electrical regs knowlege may not extend to zones and suitability of equipment

If its due to lack of space then a shower may hve to be fitted instead of the bath
What plumbers get up to, it sometimes beggars belief
 
G

Guest123

  • Thread Starter Thread Starter
  • #9
In full agreement, in my book it would costitute a code 1 on a PIR.
 
W

Wotsit

  • Thread Starter Thread Starter
  • #10
Do you think that the company that fitted it should, move it as the installation was incorrect? If so what do you think my course of action should be? I doubt a phone call the the installers detailing my concerns will suffice.
 
6

62patrick

  • Thread Starter Thread Starter
  • #11
Its a code 1 in, as in all off the above posts,
Whats the date of the installation ?,
What certificates did you get when it was installed ?
Was it a replacement boiler ?
Did anybody agree to the boiler being fitted in that position in the first place ?

When all said and done its still a code 1 in my book
 
W

WB Scott

  • Thread Starter Thread Starter
  • #12
Have you looked into the manufactureres instrustiions for the boiler? Is it suitable for purpose, ie does it have an IP rating?
 
I agree its a Code 1.

How high are your ceilings? If the boiler is above 3m then it's outside of all zones.
(I think, correct me if I'm wrong)

Mark
 
W

Wotsit

  • Thread Starter Thread Starter
  • #14
Its a code 1 in, as in all off the above posts,
Whats the date of the installation ?,
What certificates did you get when it was installed ?
Was it a replacement boiler ?
Did anybody agree to the boiler being fitted in that position in the first place ?

When all said and done its still a code 1 in my book
The date of instlation was around four years ago.

It was a new instlation.

There is a mass of paperwork, with a safety certificate for each year

My girlfriend agreed to the location of instllation but how was she to know?

I agree its a Code 1.

How high are your ceilings? If the boiler is above 3m then it's outside of all zones.
(I think, correct me if I'm wrong)

Mark
Boiler is about 35 cm above bath rim. The supply is non rcd. The fused spur is level with the bath rim, about 20 cm back from where you head is.


I would take a photo but we have tennents in there

Have you looked into the manufactureres instrustiions for the boiler? Is it suitable for purpose, ie does it have an IP rating?
Yes,

It is not sutable for instllation in a location containing a bath or shower. There is no IP raiting
 
Last edited by a moderator:
It's definately a code1 and it is something that will have to be rectified ASAP. That would surely make any insurance you have on the property invalid. I'd phone the company up that installed it and threaten to name and shame them unless they move it. Might help!