Got a combi boiler controlled by a Drayton room stat, the one you manually turn the dial round to 30 and the boiler comes on and then turn it round to 10 for it to go off, recently when I turn it round to 10 it goes off but then comes on a minute later and heats the radiators up until they are too hot to touch, only way to stop it is by isolating the boiler at the FCU, any ideas what could be causing this?
 
Is it set to pre-heat hot water from tap ?

If you turn its supply of and on , does the behavior disappear for a while ?
(the other guys will have the answer)
 
The thermostat opens and closes the Actuator Valve (Is it Y plan or S Plan ?) you should have a 3 way valve or 2 x 2 way valves controlling the water supply to the boiler and cylinder.
I would suspect ACTUATOR VALVE for heating if its not the thermostat.
 
The thermostat opens and closes the Actuator Valve (Is it Y plan or S Plan ?) you should have a 3 way valve or 2 x 2 way valves controlling the water supply to the boiler and cylinder.
I would suspect ACTUATOR VALVE for heating if its not the thermostat.
It’s a combi boiler so the above DOES NOT APPLY
 
It’s a combi boiler so the above DOES NOT APPLY
With respect,you could not say that with certainty,without seeing the system,the OP has.

It could be a right old mix-n-match? i have seen more than a few combi set-ups,with strange overide switching AND stored hot water.
 
It’s the old mechanical thermostat with a bi metal strip.... it’s just worn out. Get it replaced.

isn’t there a programmer so you can stop it coming on in the middle of the night?

might be a chance to leap into the 21st century and get one of those new fangled Smart stats.... ?
 

Reply to Combi boiler question in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

So I’ve been having this issue with my boiler for a while now, I’ve currently got one stat in the hall that when I turn it on it brings the...
Replies
4
Views
638
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
917
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
890
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock