bartkusal

-
Arms
Reaction score
36
Hello everyone and HNY.

I need clarification on this:

I been asked to change the fuse board in commercial premises, it is a sub main SP board in a basement area. The earthing cable/cpc to board is the armor of SWA cable, all circuits to the accessories has the cpc via metal conduit. I had a look at the job and the only tests I could do is Zs. The readings where in the range of 0.40-0.50 ohms, so it seems that I have fairly good Ze and R1+R2 (still to be confirmed when the isolation can take place)

I know that for new installs, you cannot have the armor or conduit as the only means of cpc, but it is only the board change and all wiring methods complied with the regs when they were installed.


So, the question is:

· Do I have to pull a new earting cable/cpc up to the board and,
· Do I have to pull in the cpc for all wiring in the final circuits


As you can understand it is a significant difference in work and cost involved and I don’t want to do it if I don’t have to. The client is a very tight as usual these days.

Thanks and best regards: Al
 
conduit is fine for earthing as long as your readings comly.
 
Hello everyone and HNY.

I need clarification on this:

I been asked to change the fuse board in commercial premises, it is a sub main SP board in a basement area. The earthing cable/cpc to board is the armor of SWA cable, all circuits to the accessories has the cpc via metal conduit. I had a look at the job and the only tests I could do is Zs. The readings where in the range of 0.40-0.50 ohms, so it seems that I have fairly good Ze and R1+R2 (still to be confirmed when the isolation can take place)

I know that for new installs, you cannot have the armor or conduit as the only means of cpc, but it is only the board change and all wiring methods complied with the regs when they were installed.


So, the question is:

· Do I have to pull a new earting cable/cpc up to the board and,
· Do I have to pull in the cpc for all wiring in the final circuits


As you can understand it is a significant difference in work and cost involved and I don’t want to do it if I don’t have to. The client is a very tight as usual these days.

Thanks and best regards: Al

Since when.. If you have proved the results comply then crack on with the board change.. Simples
 
Thanks everyone for the replies, obviously i got that wrong, i dont remember where did that came from, i did reed that somewhere, probably that was a guide or recomendation and not the regs.

I need to look in regs book more offen then.

thanks again everyone
 
Hello everyone and HNY.

the only tests I could do is Zs. The readings where in the range of 0.40-0.50 ohms, so it seems that I have fairly good Ze and R1+R2 (still to be confirmed when the isolation can take place)

/QUOTE]

You could always do an R2 as it will give a better indication of the continuity of the containment system.
 
Reg 543.2.1
" a protective conductor may consist of .............
(vi) a metal covering, for example, the sheath, screen or armouring of a cable
(vii) a metal conduit,metallic cable management system...................."
 

Reply to comercial board change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a fuseboard change I need to do soon I’m putting in a FUSEBOX 7 or 10 way RCBO+ SPD My only concern is how I should run the pyro cables in...
Replies
16
Views
1K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
778
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
731
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock