Hi there just a quick question we have wired a commercial kitchen and work tops, extract canopy, are all metal etc the whole installation will be RCD protected but will we install supplementary bonding shall it be required ? or is it OK with the use of RCD protection thanks in advance really appreciate it
 
RCDs and equipotential bonding are both measures that can protect against shock, but they protect in different ways. An RCD on the kitchen socket circuit will protect against shock from touching the line conductor of that circuit. In the event of a fault elsewhere on the system that raises the MET above true earth, the RCD won't react because it's not the socket circuit that's faulty, but the sockets' CPC will carry that raised MET voltage to all earthed appliances connected plugged into them. A shock could then occur between an appliance and the canopy, if that is connected to an extraneous duct that brings true earth into the area. Bonding the canopy ensures that whatever voltage exists, is the same on everything.
 
I don't know if the regs say anything about this specific situation, but with the kitchen you describe there will be multiple metal objects, wet hands, high current appliances, and potential paths to the outside world via service pipes.

Sounds like a high risk environment to me!
 
There is usually no requirement to earth or bond kitchen furniture unless they are actually extraneous conductive parts which I’ve never come across one which actually is.

Edit , one time a metal sink was connected to a metallic waste which went outside and into the ground but other than that.
 
Just wondering when you say "whole installation will be RCD protected" are all supplies on 30mA RCD/RCBO that offer shock protection, or are some circuits (e.g. commercial oven) on MCBs and/or 100mA/300mA RCD (fire protection, etc) in case of high leakage?
 

Reply to commercial kitchen (pub) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
675
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
802
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
266
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
695
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock