blessed day all, i have a 3PH,15HP, RPM-1775, V-230/460, AMP 37.1 Motor. Compressor Starter rating of 460VAC/ 15HP/3PH , why it keep tripping???
What are the overloads set at, what exactly is tripping, RCD MCB or the contactor itself
 
What are the overloads set at, what exactly is tripping, RCD MCB or the contactor itself
The contractor it self is whats tripping.
 

Attachments

  • IMG_2353.JPG
    369.9 KB · Views: 9
That's the overload, attached to the contactor.

The most likely fault with a compressor tripping the oveload is the compressor unloader valve sticking.
It relieves the pressure on the compressor at start up, it's what causes the air hissing at compressor switch off and start up.
 
That's the overload, attached to the contactor.

The most likely fault with a compressor tripping the oveload is the compressor unloader valve sticking.
It relieves the pressure on the compressor at start up, it's what causes the air hissing at compressor switch off and start up.
After reading your message i went and check the unloader valve, realizing that its not unloading like it should.It will spit out some then stop then spit out again then stop. Only if I turn the power (120v) off then on again it will do that. So i'm gonna take it off and see whats inside or if thats even possible. will keep you posted on progress. thanks
 
Blessed Day
I've found the issues with the compressor. There is dryer connected to the compressor and the unloader valve on the dryer constantly releases air causing the compressor not to reach it max PSI, which in return cause it to drip (overheat).
 

Reply to Compressor contactor trips in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
723
Bought an air compressor at auction. Looks to have been previously hooked up in the previous owners shop. It has two wire Romex coming from the...
Replies
2
Views
581
I have a small mechanics shop in a rural area with no access to 3 phase. I picked up a air compressor cheap and knowing at a min. I will need a...
Replies
3
Views
2K
Hi, leading on from my question the other day about running the 3 phase compressor off my 8.5kW generator I have since got my hands on a 240v to 3...
Replies
0
Views
849
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
515

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock