hi guys

ive read somewere the mounting distance for saddles when using conduit, ie how far apart they should be, cant find it anywere

any idears?

cheers
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
J

johnnyb

  • Thread Starter Thread Starter
  • #2
Not sure mate, but i think its no more than 600mm, stand to be corrected though.
 
B

bahco

  • Thread Starter Thread Starter
  • #4
i had it in my head it was no more than 1.5 mtrs for 20mm plastic....seems to far that 600 does sound about right
 
N

ninjadeathstalk

  • Thread Starter Thread Starter
  • #6
The spacing for 16<=dmm conduit is: 0.75m horizontal and 1.0m vertical for rigid metal
0.75m horizontal and 1.0m vertical for rigid insulating
0.3m horizontal and 0.5m vertical for pliable

The spacing for 16<d>=25mm conduit is: 1.75m horizontal and 2.0m vertical for rigid metal
1.5m horizontal and 1.75m vertical for rigid insulating
0.4m horizontal and 0.6m vertical for pliable

The spacing for 25<d>=40mm conduit is: 2.0m horizontal and 2.25m vertical for rigid metal
1.75m horizontal and 2.0m vertical for rigid insulating
0.6m horizontal and 0.8m vertical for pliable

The spacing for >40mm conduit is: 2.25m horizontal and 2.5m vertical for rigid metal
2.0m horizontal and 2.0m vertical for rigid insulating
0.8m horizontal and 1.0m vertical for pliable

Taken from OSG page 115 table 4C.
 