We have got a hydraulic motor/powerpack for leveling legs of a trailer. However this trailer is running off a 15KW inverter, so the motor needs to run off single phase.

The motor has come configured for 3 phase, however the motor plate does say it will run off single phase.

Would i be right in thinking it would need 2 capacitors? (start and run), and then the busbar's between W1+V1, V2+U2?
With capacitor's between U1+W2, and U2+W2?

Cheers

You don't have permission to view attachments. Attachments are hidden.

You don't have permission to view attachments. Attachments are hidden.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.
OP
M

-Matt

-
Reaction score
151
Easiest option is to run it through a VFD. It will not run from single phase, the 230V is for running in Delta which is 230 volts per phase.

I have a smaller version of that motor for running a lathe, not a bad make.

Thanks, will see if it can be exchanged for a single phase motor.
 

brianmoooore

-
Esteemed
Arms
Reaction score
2,030
I have a hydraulic four post car ramp in my workshop with a 2kW 3 phase motor, and have run it faultlessly off of a 230V single phase supply for the 20 years or so that I've had it.
I configured the motor from star to delta, added a permanently connected 'run' capacitor, and a 'start' capacitor, switched by a current operated relay.
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,533
I have a hydraulic four post car ramp in my workshop with a 2kW 3 phase motor, and have run it faultlessly off of a 230V single phase supply for the 20 years or so that I've had it.
I configured the motor from star to delta, added a permanently connected 'run' capacitor, and a 'start' capacitor, switched by a current operated relay.
and i always used to think that a 4 post ramp needed a phase each for 3 of the posts and a neutral for the 4th post. each post having the appropriate wrap of tape around it, red,yellow,blue, black. they then go up with a 120 deg. separation, wobbles the car somewhat, finds the suspension squeaks. ???
 

Darkwood

Mentor
Esteemed
Arms
Reaction score
10,044
To note here using an inverter to run single to 3ph and swapping the motor configurations will draw about 15+ amps off the supply, take that into consideration and size your mcb as stated in the drive instructions.
 
OP
M

-Matt

-
Reaction score
151
So the hydraulic manufacturer is going to send over a single phase 3KW motor the replace the 3PH one, however its rated current is 17.75A which isn't ideal, but its only used for set-up.

Is there going to be any issues with using a motor off an inverter? (have never done it), with the start up currents of the motor?

This is the inverter (its ----ing heavy!):

And 4 of these: (in 2 banks of 2)
 

ElectroChem

-
Esteemed
Arms
Reaction score
346
So the hydraulic manufacturer is going to send over a single phase 3KW motor the replace the 3PH one, however its rated current is 17.75A which isn't ideal, but its only used for set-up.

Is there going to be any issues with using a motor off an inverter? (have never done it), with the start up currents of the motor?

This is the inverter (its ----ing heavy!):

And 4 of these: (in 2 banks of 2)

I am puzzled by this.

You're using £20,000 worth of battery banks and inverters, but can't spring the few hundred quid for a 1-3 VSD to smoothly run the original motor?

Priorities much?
 

Reply to Configuring motor to run off single phase? in the Electrical Forum area at ElectriciansForums.net

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

New Posts (Please Reply)

Search Forum

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top